Section 310.15(B)(20(a) requires derating of more than 3 current carrying conductors in a cable or raceway.
Section 240.4(B) allows the next higher standard overcurrent device rating above the ampacity of the conductors being protected to be used.
Does that mean I can bundle 40 14/2 NM cables together for long distances, and connect each to a 15 amp cb?
80 current carrying conductors would require a 35% derating from 25 amps to 8.75 amps. Can I then bump the cb up to 15 amps because Section 240.6 gives me the lowest standard rated breaker as 15 amps?
Or, am I required to use a 10 amp fuse?


Earl
2017 / 2014 NEC & Related Books and Study Guides
Re: even more derating fun #97796
03/21/06 05:28 PM
03/21/06 05:28 PM
I
iwire  Offline
Moderator
Joined: Jan 2003
Posts: 4,391
North Attleboro, MA USA
IMO you could use the next standard size listed (15 amp) on any of the circuits that are not multioutlet branch circuits supplying receptacles for cord-and-plug-connected portable loads.

Of course the ampacity of the cables would still be only 8.75 amps and the connected load could not exceed that.


Bob Badger
Construction & Maintenance Electrician
Massachusetts
Re: even more derating fun #97797
03/21/06 05:57 PM
03/21/06 05:57 PM
E
earlydean  Offline OP
Member
Joined: Dec 2003
Posts: 751
Griswold, CT, USA
So, if we combine my two posts, using luminaires that do not draw more than 2 amps, I could get away with that scenenario?

12 current carrying conductors require a deration of 50%, 50% of 25 aamps is 12.5 amps. Dividing by six luminaires, gives me 2.08333 amps each.


Earl
Re: even more derating fun #97798
03/21/06 06:15 PM
03/21/06 06:15 PM
I
iwire  Offline
Moderator
Joined: Jan 2003
Posts: 4,391
North Attleboro, MA USA
Cool questions. [Linked Image]

IMO yes, 240.4(B) applies to the circuit as conditions (1), (2) and (3) are met and it tells us clearly "The next higher standard overcurrent device rating" a couple of times.

240.6 Standard Ampere Ratings shows the smallest standard rating as 15.

Bob


Bob Badger
Construction & Maintenance Electrician
Massachusetts
Re: even more derating fun #97799
03/21/06 06:47 PM
03/21/06 06:47 PM
G
George Little  Offline
Member
Joined: Jan 2004
Posts: 1,489
Michigan USA
I'm giving you guys a red sticker. Wording in the code is the "next higher standard overcurrent device" Not the next size circuit breaker. 10a. is the next size overcurrent device for earlydean's post. Guess someone is installing fuses on these circuits.


George Little
Re: even more derating fun #97800
03/21/06 07:27 PM
03/21/06 07:27 PM
Tom  Offline
Member
Joined: Jan 2001
Posts: 1,044
Shinnston, WV USA
I think that sticker should be pink instead of red, thereby giving partial credit. After all, Iwire did point out that going up to the next OCPD does not allow you to increase the ampacity (or load) of the conductors and he did correctly make the call about multioutlet circuits. These points seem to be lost on many, at least here in the Mountain State.


Few things are harder to put up with than the annoyance of a good example.
Re: even more derating fun #97801
03/21/06 07:44 PM
03/21/06 07:44 PM
I
iwire  Offline
Moderator
Joined: Jan 2003
Posts: 4,391
North Attleboro, MA USA
Interesting, I have to agree with you George, that is what it says. [Linked Image]

That aside I am not convinced the NEC intends to force the use of a fuse over a breaker.

Bob

BTW I will happily take a RED tag over a pink tag.

Pink is the color of the spare hardhats for those that always misplace their own. [Linked Image]


Bob Badger
Construction & Maintenance Electrician
Massachusetts
Re: even more derating fun #97802
03/25/06 11:09 AM
03/25/06 11:09 AM
E
earlydean  Offline OP
Member
Joined: Dec 2003
Posts: 751
Griswold, CT, USA
It takes a real manly man to wear a pink hardhat on a construction job!


Earl

Featured:

2017 Master Electrician Exam Preparation Combos
2017 NEC Electrician
Exam Prep Combos:
Master / Journeyman

 

Member Spotlight
richard
richard
L.I. New York
Posts: 95
Joined: August 2003
Show All Member Profiles 
Top Posters(30 Days)
Admin 9
Popular Topics(Views)
244,007 Are you busy
181,001 Re: Forum
171,245 Need opinion
Powered by UBB.threads™ PHP Forum Software 7.6.1
(Release build 20180101)
Page Time: 0.020s Queries: 14 (0.003s) Memory: 0.9930 MB (Peak: 1.1522 MB) Zlib enabled. Server Time: 2018-02-18 05:01:13 UTC