Industrial Luminaires #97617
03/06/06 09:24 PM
03/06/06 09:24 PM
ShockMe77  Offline OP
Joined: Jun 2005
Posts: 821
Rahway, New Jersey
I have a few fluorescent STYLE 'L' lights to hang and I was going to wire them using 14-3 SJ cord. Upon further review of the job, and the wiring method, I'm not sure if I will compy with code.

The lights will hang on jackchain that'll be attached to joists above a suspended ceiling. I want to tie-wrap the cord to the jackchain and run it through the ceiling to the junction box so the job will look as neat as possible. Article 400.7 (2) says cords can be used for luminaires, but article 400.8 (3) forbids running cords through a suspended ceiling. What should I do?

[This message has been edited by ShockMe77 (edited 03-06-2006).]

2017 / 2014 NEC & Related Books and Study Guides
Re: Industrial Luminaires #97618
03/06/06 09:31 PM
03/06/06 09:31 PM
earlydean  Offline
Joined: Dec 2003
Posts: 751
Griswold, CT, USA
Don't use a cord, use AC or MC.

Re: Industrial Luminaires #97619
03/08/06 04:17 AM
03/08/06 04:17 AM
Tesla  Offline
Joined: Jun 2004
Posts: 1,273
Sacramento, CA
What looks neat and meets Code: mount a receptacle within a junction box in the soft lid.

CADDY and B-Line make supports for it. (512)

Then just plug the SOJ into the receptacle.

SO/ SOJ cannot go above the lid: not rated for the heat up there.

The run from the receptacle junction box to the branch circuit would normally be MC.

A seismic wire to sustain the j-box would also be in order.

Otherwise, go all of the way with MC/ Greenfield. It looks nasty going through the lid. But it costs less.

You choose.

Re: Industrial Luminaires #97620
03/08/06 11:23 AM
03/08/06 11:23 AM
ShockMe77  Offline OP
Joined: Jun 2005
Posts: 821
Rahway, New Jersey
Thanks for the replies, guys. I am going to come down with 12-2 MC at each fixture and do whatever splicing necessary in the ceiling above. I was just curious as to why the cord couldn't be run through the drop-ceiling (heat), now I know why. Thanks.


2017 Master Electrician Exam Preparation Combos
2017 NEC Electrician
Exam Prep Combos:
Master / Journeyman


Member Spotlight
kamloops BC Canada
Posts: 1,143
Joined: May 2003
Show All Member Profiles 
Top Posters(30 Days)
Admin 5
Trumpy 5
Popular Topics(Views)
244,860 Are you busy
181,981 Re: Forum
172,016 Need opinion
Powered by UBB.threads™ PHP Forum Software 7.6.1
(Release build 20180101)
Page Time: 0.022s Queries: 14 (0.005s) Memory: 0.9587 MB (Peak: 1.0895 MB) Zlib enabled. Server Time: 2018-03-23 03:16:32 UTC