Clean Ground #97305
02/16/06 05:25 PM
02/16/06 05:25 PM
G
George Little  Offline OP
Member
Joined: Jan 2004
Posts: 1,489
Michigan USA
A contractor wants to have a "clean ground" at a location about 100' from the Service. The panel located 100' from the Service is being fed using a metal raceway as the EGC. Can the contractor just tie wrap an insulated conductor to the exterior of the conduit and use this conductor as his "clean ground"? I said No but need a code reference to back me up.


George Little
2017 / 2014 NEC & Related Books and Study Guides
Re: Clean Ground #97306
02/16/06 06:09 PM
02/16/06 06:09 PM
G
gfretwell  Offline

Member
Joined: Jul 2004
Posts: 9,242
Estero,Fl,usa
You can always say raceways are not to be used as "support" of other wiring methods but that is a pretty thin beef. Why isn't he just running it in the pipe? Even back in the olden days when IBM liked IG outlets we let them run with the circuit conductors. I suspect mythology has trumped reason with this guy.


Greg Fretwell
Re: Clean Ground #97307
02/17/06 01:26 PM
02/17/06 01:26 PM
R
resqcapt19  Offline
Member
Joined: Nov 2000
Posts: 2,148
IL
George,
The clean ground is still an EGC and must be in the raceway with the other circuit conductors. 300.3(B). The rule cited by Greg also applies. Is he trying to install an illegal "isolated" ground?
Don


Don(resqcapt19)
Re: Clean Ground #97308
02/17/06 04:05 PM
02/17/06 04:05 PM
P
PCBelarge  Offline
Member
Joined: Jun 2003
Posts: 681
Dobbs Ferry, NY, USA
250.146(D)Isolated Receptacles.

The receptacle grounding terminal shall be grounded by an insulated equipment grounding conductor RUN WITH THE CIRCUIT CONDUCTORS.


Pierre Belarge
Re: Clean Ground #97309
02/17/06 05:42 PM
02/17/06 05:42 PM
L
Larry Fine  Offline
Member
Joined: Feb 2005
Posts: 693
Richmond, VA
Define "with".


Larry Fine
Fine Electric Co.
fineelectricco.com
Re: Clean Ground #97310
02/18/06 12:28 PM
02/18/06 12:28 PM
G
gfretwell  Offline

Member
Joined: Jul 2004
Posts: 9,242
Estero,Fl,usa
That was my thought too Larry.


Greg Fretwell
Re: Clean Ground #97311
02/18/06 12:44 PM
02/18/06 12:44 PM
G
George Little  Offline OP
Member
Joined: Jan 2004
Posts: 1,489
Michigan USA
Use as it is in this location of the code it becomes a subjective word and in my mind it means in the same raceway, cable or trench.

There is a condition for running the grounding conductor separate from the other conductors as defined in 250.130(C) for receptacles and extentions and I would accept a single conductor for that type of installation. For example where it is a NM cable job. But after seeing what you guy/gals have posted I'm convinced that the proper installation would be to have the IG installed in the same wiring method as discribed above.


George Little
Re: Clean Ground #97312
02/18/06 02:21 PM
02/18/06 02:21 PM
I
iwire  Offline
Moderator
Joined: Jan 2003
Posts: 4,391
North Attleboro, MA USA
George this 'clean' ground still must be tired into the systems grounded conductor at some point.

What exactly is going on here?


Bob Badger
Construction & Maintenance Electrician
Massachusetts
Re: Clean Ground #97313
02/18/06 02:27 PM
02/18/06 02:27 PM
G
gfretwell  Offline

Member
Joined: Jul 2004
Posts: 9,242
Estero,Fl,usa
I agree George. I am just afraid you will get tangled up in the mythology that got this guy's panties in a wad about the "clean ground" in the first place. You may hear the definition of "with" thrown around.
You can certainly toss back that the inside of the raceway is a "cleaner" environment than the outside but that is probably beyond the scope of your job.
Is this ground going to be protecting the case of metal equipment or is it just for his electronics in an insulated box. That could be the deciding factor about whether it requires the mechanical protection the raceway provides.


Greg Fretwell
Re: Clean Ground #97314
02/18/06 02:39 PM
02/18/06 02:39 PM
G
gfretwell  Offline

Member
Joined: Jul 2004
Posts: 9,242
Estero,Fl,usa
BTW one of the arguments I have heard against IG is that the "one way" penetrations through metal cabinets and raceways that are not bonded at both ends actually creates a choke that reduces the effectiveness of the IG. (similar to GECs)
IBM decided it was better to bond the hell out of everything. In the 60s we had single point grounding and we had to do a "baseplate ground" <continuity> check, lifting the single point ground and verifying that was the only path to ground.
After all the engineering changes were installed that "single point" was getting up to 20 or 30 additional grounding wires (added to fix problems) we had to remove to clear all paths to ground and sanity finaly won out. They stopped thinking star grounding was important. It was about that time that the IG dissapeared from the physical planning manual. In your typical PC you will have lots of DC to AC ground points once you start hooking up I/O.


Greg Fretwell
Page 1 of 2 1 2

Featured:

2017 Master Electrician Exam Preparation Combos
2017 NEC Electrician
Exam Prep Combos:
Master / Journeyman

 

Member Spotlight
waymag
waymag
dallas, texas, USA
Posts: 68
Joined: January 2002
Show All Member Profiles 
Top Posters(30 Days)
Admin 5
Popular Topics(Views)
248,132 Are you busy
185,587 Re: Forum
174,922 Need opinion
Powered by UBB.threads™ PHP Forum Software 7.6.1
(Release build 20180101)
Page Time: 0.033s Queries: 15 (0.005s) Memory: 1.0253 MB (Peak: 1.2022 MB) Zlib enabled. Server Time: 2018-07-19 18:58:52 UTC