manual override switch #97275
02/13/06 10:30 AM
02/13/06 10:30 AM
B
bobjodd  Offline OP
Junior Member
Joined: Feb 2002
Posts: 4
grand rapids michigan USA
I was doing some trouble shooting for the hall lights in a 3 story appartment complex. On one floor there was a photo eye by a window.When the sun came up it shut the hall lights off It worked fine.
My question is doesn't this hall lighting circuit with the photo eye have to have an override switch??????????

2017 / 2014 NEC & Related Books and Study Guides
Re: manual override switch #97276
02/13/06 12:37 PM
02/13/06 12:37 PM
X
XtheEdgeX  Offline
Member
Joined: Apr 2005
Posts: 116
Florida
According to 210.70, it does not. BUT, Life Safety Codes require egress lighting to be installed, and they can not be turned off by the sensor or a wall switch.

Re: manual override switch #97277
02/13/06 01:53 PM
02/13/06 01:53 PM
G
gfretwell  Offline

Member
Joined: Jul 2004
Posts: 9,298
Estero,Fl,usa
How do they rationalize this with the energy code?


Greg Fretwell
Re: manual override switch #97278
02/13/06 04:15 PM
02/13/06 04:15 PM
I
iwire  Offline
Moderator
Joined: Jan 2003
Posts: 4,391
North Attleboro, MA USA
Greg per the NEC you can not switch off any legally required emergency lighting unless it is rigged to come back on automatically regardless of the switch position during a power failure. Sorry I am not at my computer with the NEC in it for a section number.

Typically we accomplish this via normally closed contacters.

I think safety codes trump energy codes.

Bob


Bob Badger
Construction & Maintenance Electrician
Massachusetts
Re: manual override switch #97279
02/13/06 05:33 PM
02/13/06 05:33 PM
G
gfretwell  Offline

Member
Joined: Jul 2004
Posts: 9,298
Estero,Fl,usa
I usually think of that kind of lighting being the battery lights. I was curious if energy codes affect lighting in places where it is not necessary to be 24/7 because of ambient light.


Greg Fretwell
Re: manual override switch #97280
02/13/06 05:38 PM
02/13/06 05:38 PM
I
iwire  Offline
Moderator
Joined: Jan 2003
Posts: 4,391
North Attleboro, MA USA
I hear you Greg, we run in to this in a lot of new installations, many new buildings have ambient light sensors used to kill the electric lights when the natural light is enough.

We are switching more of the required lighting down but as I mentioned this usually involves adding some NC contactors that drop closed on utility power loss.

Bob


Bob Badger
Construction & Maintenance Electrician
Massachusetts
Re: manual override switch #97281
02/13/06 08:27 PM
02/13/06 08:27 PM
E
earlydean  Offline
Member
Joined: Dec 2003
Posts: 751
Griswold, CT, USA
The Life Safety Code (NFPA 101) does not necessarily require lights to be on during the day. It only requires that there be a minimum level of lighting along the exit path whenever the building is occupied. If this lighting is supplied by daylight, then we have met the Life Safety Code.


Earl
Re: manual override switch #97282
02/13/06 08:44 PM
02/13/06 08:44 PM
E
earlydean  Offline
Member
Joined: Dec 2003
Posts: 751
Griswold, CT, USA
The IBC also has something to say on this subject:

"1006.1 Illumination required. The means of egress, including the exit discharge, shall be illuminated at all times the building space served by the means of egress is occupied.
Exceptions:
1. Occupancies in Group U.
2. Aisle accessways in Group A.
3. Dwelling units and sleeping units in Groups R-1, R-2 and R-3.
4. Sleeping units of Group I occupancies.

1006.2 Illumination level. The means of egress illumination level shall not be less than 1 foot-candle (11 lux) at the floor level."

By the way, safety codes do not "trump" energy codes. We need to find a way to satisfy both codes if at all possible. If not possible because of conflicting rules, then the adopting authority needs to be consulted to make the call.


Earl
Re: manual override switch #97283
02/13/06 09:33 PM
02/13/06 09:33 PM
I
iwire  Offline
Moderator
Joined: Jan 2003
Posts: 4,391
North Attleboro, MA USA
Quote
By the way, safety codes do not "trump" energy codes. We need to find a way to satisfy both codes if at all possible. If not possible because of conflicting rules, then the adopting authority needs to be consulted to make the call.


And that AHJ is going to decide that energy codes are on the bottom of the list in regards to importance. [Linked Image]


Bob Badger
Construction & Maintenance Electrician
Massachusetts
Re: manual override switch #97284
02/13/06 09:55 PM
02/13/06 09:55 PM
G
gfretwell  Offline

Member
Joined: Jul 2004
Posts: 9,298
Estero,Fl,usa
Quote
And that AHJ is going to decide that energy codes are on the bottom of the list in regards to importance.


We can only hope but when I see some of the other stuff going on (like California) I am not sure.
Actually I am ahead of that curve with lots of low level lights on occupancy sensors. The only bright lights we have are task lighting.


Greg Fretwell
Page 1 of 3 1 2 3

Featured:

2017 Master Electrician Exam Preparation Combos
2017 NEC Electrician
Exam Prep Combos:
Master / Journeyman

 

Member Spotlight
Posts: 362
Joined: April 2003
Show All Member Profiles 
Top Posters(30 Days)
sparky 11
Popular Topics(Views)
250,474 Are you busy
188,046 Re: Forum
177,671 Need opinion
Powered by UBB.threads™ PHP Forum Software 7.6.1
(Release build 20180101)
Page Time: 0.043s Queries: 15 (0.004s) Memory: 1.0268 MB (Peak: 1.2043 MB) Zlib enabled. Server Time: 2018-10-20 02:12:41 UTC