250.70 GEC to electrode connection. #97158
01/26/06 09:11 PM
01/26/06 09:11 PM
E
e57  Offline OP
Member
Joined: May 2003
Posts: 2,876
S.F.,CA USA
We have talked about this before I think....

Connection to Ufer grounds... If you are using CU wire (over #4)as your Concrete Encased Electrode, (Instead of rebar) would a split bolt connecting the GEC to the panel be considered a "Splice" in the GEC according to 250.64(C)?

At what point would a wire Ufer become a GEC?

(It is accessible for 250.68)

Or would it be 250.70, as most other connections to electrodes are?

Quote
250.70 Methods of Grounding and Bonding Conductor Connection to Electrodes.
The grounding or bonding conductor shall be connected to the grounding electrode by exothermic welding, listed lugs, listed pressure connectors, listed clamps, or other listed means. Connections depending on solder shall not be used. Ground clamps shall be listed for the materials of the grounding electrode and the grounding electrode conductor and, where used on pipe, rod, or other buried electrodes, shall also be listed for direct soil burial or concrete encasement. Not more than one conductor shall be connected to the grounding electrode by a single clamp or fitting unless the clamp or fitting is listed for multiple conductors. One of the following methods shall be used:
(1) A pipe fitting, pipe plug, or other approved device screwed into a pipe or pipe fitting
(2) A listed bolted clamp of cast bronze or brass, or plain or malleable iron
(3) For indoor telecommunications purposes only, a listed sheet metal strap-type ground clamp having a rigid metal base that seats on the electrode and having a strap of such material and dimensions that it is not likely to stretch during or after installation
(4) An equally substantial approved means


------------------------------------------
Forgot local code:
Quote

250-50. Grounding Electrode System. If available on the premises at each building or structure served, each item (a) through (d) below, and any made electrodes in accordance with Sections 250-52(c) and (d), shall be bonded together to form the grounding electrode system. A concrete- encased electrode as defined by Section 250-50(c) shall be installed at each new building or structure, and for existing buildings or structures when a new or replacement foundation footing with a perimeter length of 20 feet (6.096 m)is installed. The bonding jumper(s) shall be installed in accordance with Sections 250-64(a), (b) and (e), shall be sized in accordance with Section 250-66 and shall be connected in the manner specified in Section 250-70.


So what do you think, Split Bolt behind a 2G ring OK?

[This message has been edited by e57 (edited 01-26-2006).]


Mark Heller
"Well - I oughta....." -Jackie Gleason
2017 / 2014 NEC & Related Books and Study Guides
Re: 250.70 GEC to electrode connection. #97159
01/27/06 12:22 AM
01/27/06 12:22 AM
G
gfretwell  Offline

Member
Joined: Jul 2004
Posts: 9,242
Estero,Fl,usa
I think if it looks like a GEC it is a GEC and can't be spliced but your mileage may vary. I can also see the point that it might be the electrode you are splicing to.


Greg Fretwell
Re: 250.70 GEC to electrode connection. #97160
01/27/06 12:44 AM
01/27/06 12:44 AM
G
gfretwell  Offline

Member
Joined: Jul 2004
Posts: 9,242
Estero,Fl,usa
I think, if you drove a rod and ran an unspliced #4 to it you could splice this Ufer GEC to the unspliced one, no questions.
Is that cheaper than a cadweld shot?
Maybe you could just sweet talk the POCO guy into crimping one of his fancy irreversible compression connectors in there to splice it.


Greg Fretwell

Featured:

2017 Master Electrician Exam Preparation Combos
2017 NEC Electrician
Exam Prep Combos:
Master / Journeyman

 

Member Spotlight
dougwells
dougwells
kamloops BC Canada
Posts: 1,145
Joined: May 2003
Show All Member Profiles 
Top Posters(30 Days)
Admin 5
Popular Topics(Views)
248,157 Are you busy
185,628 Re: Forum
174,988 Need opinion
Powered by UBB.threads™ PHP Forum Software 7.6.1
(Release build 20180101)
Page Time: 0.018s Queries: 14 (0.003s) Memory: 0.9541 MB (Peak: 1.0782 MB) Zlib enabled. Server Time: 2018-07-22 05:08:13 UTC