emergency electric rm. #97141
01/25/06 05:46 PM
01/25/06 05:46 PM
jmcelectric  Offline OP
Joined: Jan 2004
Posts: 16
Is it ok to run a 4" feeder for a 400a normal power panel through an emergency electric room,or do i need a 2hr seperation? I can't find it anywhere in the code that says i can't.Thanks

2017 / 2014 NEC & Related Books and Study Guides
Re: emergency electric rm. #97142
01/29/06 09:46 PM
01/29/06 09:46 PM
tdhorne  Offline
Joined: Mar 2001
Posts: 345
Maryland, USA
The US NEC only forbids placing both emergency and non emergency conductors in the same raceway or box. It is silent on separating the raceways so it must be a building code issue.
Tom Horne

Tom Horne

"This alternating current stuff is just a fad. It is much too dangerous for general use" Thomas Alva Edison
Re: emergency electric rm. #97143
01/30/06 10:07 AM
01/30/06 10:07 AM
Ryan_J  Offline
Joined: Aug 2003
Posts: 1,374
West Jordan, Utah, USA
It is not a building code issue. I think it is fine.

Ryan Jackson,
Salt Lake City
Re: emergency electric rm. #97144
01/30/06 04:16 PM
01/30/06 04:16 PM
earlydean  Offline
Joined: Dec 2003
Posts: 751
Griswold, CT, USA
The IBC Section 302.1.1 covers incidental Use Areas. The only electrical only type incidental use requiring a fire rated barrier wall and floor/ceiling assemblies is for stationary lead-acid battery rooms having a liquid capacity of more than 100 gallons used for facility standby power, emergency power or interrupted power supplies.
These rooms require a 1 hour rating for Group B, F, H, M, S and U occupancies and a 2 hours rating for Group A, E, I and R occupancies.

Other common incidental use areas would be: furnace rooms, boiler rooms, refrigerant rooms, parking garages, incinerator rooms, paint shops, laboratories and vocational shops, also laundry rooms, waste and linen collection rooms and storage rooms over 100 square feet, and padded cells.

Re: emergency electric rm. #97145
01/30/06 04:21 PM
01/30/06 04:21 PM
earlydean  Offline
Joined: Dec 2003
Posts: 751
Griswold, CT, USA
It may be that your particular electrical room is backed up to a fire area or separation wall. In that case the fire rating will have to extend from floor to ceiling. Any penetrations will have to be closed in a proper manner.



2017 Master Electrician Exam Preparation Combos
2017 NEC Electrician
Exam Prep Combos:
Master / Journeyman


Member Spotlight
Attic Rat
Attic Rat
Bergen Co.,N.J. USA
Posts: 524
Joined: December 2003
Show All Member Profiles 
Top Posters(30 Days)
Admin 5
Trumpy 5
Popular Topics(Views)
244,398 Are you busy
181,512 Re: Forum
171,562 Need opinion
Powered by UBB.threads™ PHP Forum Software 7.6.1
(Release build 20180101)
Page Time: 0.012s Queries: 14 (0.003s) Memory: 0.9667 MB (Peak: 1.1058 MB) Zlib enabled. Server Time: 2018-03-18 11:53:30 UTC