#97141 - 01/25/06 04:46 PM emergency electric rm.  
jmcelectric  Offline
Member
Joined: Jan 2004
Posts: 16
Is it ok to run a 4" feeder for a 400a normal power panel through an emergency electric room,or do i need a 2hr seperation? I can't find it anywhere in the code that says i can't.Thanks


2017 / 2014 NEC & Related Books and Study Guides

#97142 - 01/29/06 08:46 PM Re: emergency electric rm.  
tdhorne  Offline
Member
Joined: Mar 2001
Posts: 345
Maryland, USA
The US NEC only forbids placing both emergency and non emergency conductors in the same raceway or box. It is silent on separating the raceways so it must be a building code issue.
--
Tom Horne


Tom Horne

"This alternating current stuff is just a fad. It is much too dangerous for general use" Thomas Alva Edison

#97143 - 01/30/06 09:07 AM Re: emergency electric rm.  
Ryan_J  Offline
Moderator
Joined: Aug 2003
Posts: 1,374
West Jordan, Utah, USA
It is not a building code issue. I think it is fine.


Ryan Jackson,
Salt Lake City

#97144 - 01/30/06 03:16 PM Re: emergency electric rm.  
earlydean  Offline
Member
Joined: Dec 2003
Posts: 751
Griswold, CT, USA
The IBC Section 302.1.1 covers incidental Use Areas. The only electrical only type incidental use requiring a fire rated barrier wall and floor/ceiling assemblies is for stationary lead-acid battery rooms having a liquid capacity of more than 100 gallons used for facility standby power, emergency power or interrupted power supplies.
These rooms require a 1 hour rating for Group B, F, H, M, S and U occupancies and a 2 hours rating for Group A, E, I and R occupancies.

Other common incidental use areas would be: furnace rooms, boiler rooms, refrigerant rooms, parking garages, incinerator rooms, paint shops, laboratories and vocational shops, also laundry rooms, waste and linen collection rooms and storage rooms over 100 square feet, and padded cells.


Earl

#97145 - 01/30/06 03:21 PM Re: emergency electric rm.  
earlydean  Offline
Member
Joined: Dec 2003
Posts: 751
Griswold, CT, USA
It may be that your particular electrical room is backed up to a fire area or separation wall. In that case the fire rating will have to extend from floor to ceiling. Any penetrations will have to be closed in a proper manner.


Earl


Member Spotlight
The_Lightman
The_Lightman
Orlando, Fl, USA
Posts: 49
Joined: August 2001
Show All Member Profiles 
Featured:

2017 Master Electrician Exam Preparation Combos
2017 NEC Electrician
Exam Prep Combos:
Master / Journeyman

 

Shout Box
Powered by UBB.threads™ PHP Forum Software 7.6.0
Page Time: 0.014s Queries: 14 (0.003s) Memory: 0.7682 MB (Peak: 0.9073 MB) Zlib enabled. Server Time: 2017-12-15 21:33:21 UTC