ECN Electrical Forum - Discussion Forums for Electricians, Inspectors and Related Professionals
ECN Shout Chat
Shout Box
Recent Posts
Changing a Bulb
by gfretwell. 07/14/18 03:12 PM
Tray cable?
by gfretwell. 07/11/18 10:18 PM
Eaton Heavy Duty 30A and 60A Safety Switches
by Admin. 07/11/18 09:49 PM
ORTOVOX Recalls Avalanche Transceivers
by Admin. 07/11/18 09:44 PM
Tingle off the water spigot
by gfretwell. 07/08/18 12:58 PM
New in the Gallery:
Plug terminals
Housebilding DIY wiring
Who's Online Now
0 registered members (), 9 guests, and 16 spiders.
Key: Admin, Global Mod, Mod
Previous Thread
Next Thread
Print Thread
Rate Thread
emergency electric rm. #97141
01/25/06 05:46 PM
01/25/06 05:46 PM
J
jmcelectric  Offline OP
Member
Joined: Jan 2004
Posts: 16
Is it ok to run a 4" feeder for a 400a normal power panel through an emergency electric room,or do i need a 2hr seperation? I can't find it anywhere in the code that says i can't.Thanks

2017 / 2014 NEC & Related Books and Study Guides
Re: emergency electric rm. #97142
01/29/06 09:46 PM
01/29/06 09:46 PM
T
tdhorne  Offline
Member
Joined: Mar 2001
Posts: 345
Maryland, USA
The US NEC only forbids placing both emergency and non emergency conductors in the same raceway or box. It is silent on separating the raceways so it must be a building code issue.
--
Tom Horne


Tom Horne

"This alternating current stuff is just a fad. It is much too dangerous for general use" Thomas Alva Edison
Re: emergency electric rm. #97143
01/30/06 10:07 AM
01/30/06 10:07 AM
R
Ryan_J  Offline
Moderator
Joined: Aug 2003
Posts: 1,374
West Jordan, Utah, USA
It is not a building code issue. I think it is fine.


Ryan Jackson,
Salt Lake City
Re: emergency electric rm. #97144
01/30/06 04:16 PM
01/30/06 04:16 PM
E
earlydean  Offline
Member
Joined: Dec 2003
Posts: 751
Griswold, CT, USA
The IBC Section 302.1.1 covers incidental Use Areas. The only electrical only type incidental use requiring a fire rated barrier wall and floor/ceiling assemblies is for stationary lead-acid battery rooms having a liquid capacity of more than 100 gallons used for facility standby power, emergency power or interrupted power supplies.
These rooms require a 1 hour rating for Group B, F, H, M, S and U occupancies and a 2 hours rating for Group A, E, I and R occupancies.

Other common incidental use areas would be: furnace rooms, boiler rooms, refrigerant rooms, parking garages, incinerator rooms, paint shops, laboratories and vocational shops, also laundry rooms, waste and linen collection rooms and storage rooms over 100 square feet, and padded cells.


Earl
Re: emergency electric rm. #97145
01/30/06 04:21 PM
01/30/06 04:21 PM
E
earlydean  Offline
Member
Joined: Dec 2003
Posts: 751
Griswold, CT, USA
It may be that your particular electrical room is backed up to a fire area or separation wall. In that case the fire rating will have to extend from floor to ceiling. Any penetrations will have to be closed in a proper manner.


Earl

Featured:

2017 Master Electrician Exam Preparation Combos
2017 NEC Electrician
Exam Prep Combos:
Master / Journeyman

 

Member Spotlight
Admin
Admin
NY, USA
Posts: 3,503
Joined: October 2000
Show All Member Profiles 
Top Posters(30 Days)
Admin 5
Popular Topics(Views)
248,146 Are you busy
185,612 Re: Forum
174,948 Need opinion
Powered by UBB.threads™ PHP Forum Software 7.6.1
(Release build 20180101)
Page Time: 0.018s Queries: 14 (0.004s) Memory: 0.9673 MB (Peak: 1.1065 MB) Zlib enabled. Server Time: 2018-07-21 00:08:24 UTC