ECN Electrical Forum - Discussion Forums for Electricians, Inspectors and Related Professionals

>> Home   >> Electrical-Photos   >> Classifieds   >> Subscribe to Newsletter   >> Store  
 

Featured:

 Electrical
 Clearance

 *
 Tools
 *

 Books

 *

 Test Equipment

 

Recent Gallery Topics:
What in Tarnation?
What in Tarnation?
by timmp, September 10
Plumber meets Electrician
Plumber meets Electrician
by timmp, September 10
Who's Online Now
0 members (), 165 guests, and 19 robots.
Key: Admin, Global Mod, Mod
Previous Thread
Next Thread
Print Thread
Rate Thread
#97141 01/25/06 05:46 PM
Joined: Jan 2004
Posts: 16
J
Member
Is it ok to run a 4" feeder for a 400a normal power panel through an emergency electric room,or do i need a 2hr seperation? I can't find it anywhere in the code that says i can't.Thanks

Work Gear for Electricians and the Trades

Workgear for Electricians

#97142 01/29/06 09:46 PM
Joined: Mar 2001
Posts: 345
T
Member
The US NEC only forbids placing both emergency and non emergency conductors in the same raceway or box. It is silent on separating the raceways so it must be a building code issue.
--
Tom Horne


Tom Horne

"This alternating current stuff is just a fad. It is much too dangerous for general use" Thomas Alva Edison
#97143 01/30/06 10:07 AM
Joined: Aug 2003
Posts: 1,374
R
Moderator
It is not a building code issue. I think it is fine.


Ryan Jackson,
Salt Lake City
#97144 01/30/06 04:16 PM
Joined: Dec 2003
Posts: 751
E
Member
The IBC Section 302.1.1 covers incidental Use Areas. The only electrical only type incidental use requiring a fire rated barrier wall and floor/ceiling assemblies is for stationary lead-acid battery rooms having a liquid capacity of more than 100 gallons used for facility standby power, emergency power or interrupted power supplies.
These rooms require a 1 hour rating for Group B, F, H, M, S and U occupancies and a 2 hours rating for Group A, E, I and R occupancies.

Other common incidental use areas would be: furnace rooms, boiler rooms, refrigerant rooms, parking garages, incinerator rooms, paint shops, laboratories and vocational shops, also laundry rooms, waste and linen collection rooms and storage rooms over 100 square feet, and padded cells.


Earl
#97145 01/30/06 04:21 PM
Joined: Dec 2003
Posts: 751
E
Member
It may be that your particular electrical room is backed up to a fire area or separation wall. In that case the fire rating will have to extend from floor to ceiling. Any penetrations will have to be closed in a proper manner.


Earl

Link Copied to Clipboard
Powered by UBB.threads™ PHP Forum Software 7.7.5