#97095 - 01/19/06 09:32 PM Conductor Size  
Sparky_1  Offline
Member
Joined: Nov 2004
Posts: 14
What is the smallest size feeder and neutral that I can use in this situation?

I have a fat storage tank that has a Control panel that feeds a 4500 watt / 240 volt heating element,
7 1/2 HP 3 phase motor 240 V (20.5 amps), fractional hp circulating pump 1/2 amp,
convenience outlet and light. Roughly 40 amps, with the nameplate of the fat tank control panel at 65 amps. ( The tank company stated that the 125% of FLA was listed on the FLA
sticker) The control circuit is fused down to 15 amps 120 volt.

We have 480 Volt 3 phase, so I set a 30 kva transformer feeding a 100 amp 240 Volt disconnect.
Can I feed this control panel with # 6 THHN fused at 70 amps and reduce the neutral to a # 12,or does it have to be a # 6?. Or do I have to run # 4s THHN to this unit?

[This message has been edited by Sparky_1 (edited 01-19-2006).]


2017 / 2014 NEC & Related Books and Study Guides

#97096 - 01/20/06 01:22 AM Re: Conductor Size  
gfretwell  Online Content


Member
Joined: Jul 2004
Posts: 9,123
Estero,Fl,usa
If I was answering a question on a test I would say the #6 THHN fused at 70a (using the round up rule) with a #12 neutral serving 1 or 2 single pole 20a breakers on different phases is the minimum. I can't say that is the best design decision.


Greg Fretwell

#97097 - 01/20/06 06:51 PM Re: Conductor Size  
Sparky_1  Offline
Member
Joined: Nov 2004
Posts: 14
Everything worked out today, we ran # 6s with a separate 15 amp control circuit.
I threw a amp meter on the unit, the FLA was 41.
The inspector wants a sticker stating that is has two separate disconnects.



Member Spotlight
Theelectrikid
Theelectrikid
Levittown, PA
Posts: 810
Joined: April 2004
Show All Member Profiles 
Featured:

2017 Master Electrician Exam Preparation Combos
2017 NEC Electrician
Exam Prep Combos:
Master / Journeyman

 

Shout Box
Powered by UBB.threads™ PHP Forum Software 7.6.0
Page Time: 0.012s Queries: 14 (0.003s) Memory: 0.7524 MB (Peak: 0.8731 MB) Zlib enabled. Server Time: 2017-10-21 06:23:54 UTC