Machinery Ground rods #96236
11/10/05 07:36 PM
11/10/05 07:36 PM
D
Dnkldorf  Offline OP
Member
Joined: Dec 2004
Posts: 1,064
nowhere usa
Walked into a plant this afternoon, to quote some work, and I am still noticing guys installing CNC machines, lathes, and such with ground rods by the machines.

I know manufacturers "require" this but the NEC is still somewhat unclear.

Under some excemptions you can put a ground rod if you want but the EGC from the feeder must be tied to it. You can't connect the ground rod by itself to the equipment without that being tied to the service ground.

See where i am going, I hope...

I remove them when I find them, after checking that an EGC was installed.

Am I on the right track?


Dnk.....

2017 / 2014 NEC & Related Books and Study Guides
Re: Machinery Ground rods #96237
11/10/05 07:49 PM
11/10/05 07:49 PM
R
resqcapt19  Offline
Member
Joined: Nov 2000
Posts: 2,148
IL
As long as there is an EGC run with the power conductors and connected to the equipment there is no reason to remove the rods. They do not have any adverse effect.
Don


Don(resqcapt19)
Re: Machinery Ground rods #96238
11/10/05 07:50 PM
11/10/05 07:50 PM
Tom  Offline
Member
Joined: Jan 2001
Posts: 1,044
Shinnston, WV USA
If the machine is properly grounded by an equipment ground run with or enclosing the conductors to the machine, then I see no reason to remove the supplementary electrode.

If the rod is required by the installation instructions furnished by the manufacturer of listed equipment, then it is part of the listing and labeling and should remain in place.

Tom


Few things are harder to put up with than the annoyance of a good example.
Re: Machinery Ground rods #96239
11/10/05 07:51 PM
11/10/05 07:51 PM
I
iwire  Offline
Moderator
Joined: Jan 2003
Posts: 4,391
North Attleboro, MA USA
As long as the equipment is grounded to the source as required by the NEC they can add as many 'extra pointless' (supplementary) rods at machine.

Quote
250.54 Supplementary Grounding Electrodes.
Supplementary grounding electrodes shall be permitted to be connected to the equipment grounding conductors specified in 250.118 and shall not be required to comply with the electrode bonding requirements of 250.50 or 250.53(C) or the resistance requirements of 250.56, but the earth shall not be used as the sole equipment grounding conductor.


Notice that to the NEC Supplementary is entirely different than Supplemental


Bob Badger
Construction & Maintenance Electrician
Massachusetts
Re: Machinery Ground rods #96240
11/10/05 08:10 PM
11/10/05 08:10 PM
D
Dnkldorf  Offline OP
Member
Joined: Dec 2004
Posts: 1,064
nowhere usa
Well, 2 things bother me,
One is the obviuos trip hazzard they posses.
Some of them run across the floor 5-6 feet, to where the ground rod was driven.

The second being, in part to how many I have seen wrong. This is where they didn't pull a EGC, and the ground buss bar inside the equipment was tied to the ground rod only.


Dnk...

Re: Machinery Ground rods #96241
11/10/05 08:45 PM
11/10/05 08:45 PM
electure  Offline

Member
Joined: Dec 2000
Posts: 4,274
Fullerton, CA USA
Quote
This is where they didn't pull a EGC, and the ground buss bar inside the equipment was tied to the ground rod only.


Keep in mind that an EGC doesn't necessarily have to be pulled.
Conduit also can be considered as the EGC under 250.118. "Wire" is only one of the fourteen acceptable items listed.


Featured:

2017 Master Electrician Exam Preparation Combos
2017 NEC Electrician
Exam Prep Combos:
Master / Journeyman

 

Member Spotlight
Tom
Tom
Shinnston, WV USA
Posts: 1,044
Joined: January 2001
Show All Member Profiles 
Top Posters(30 Days)
sparky 11
Popular Topics(Views)
250,580 Are you busy
188,116 Re: Forum
177,764 Need opinion
Powered by UBB.threads™ PHP Forum Software 7.6.1
(Release build 20180101)
Page Time: 0.037s Queries: 14 (0.005s) Memory: 0.9782 MB (Peak: 1.1245 MB) Zlib enabled. Server Time: 2018-10-22 05:41:24 UTC