Bonding water pipe #96171
11/07/05 10:43 AM
11/07/05 10:43 AM
S
sid123456  Offline OP
Member
Joined: Jan 2005
Posts: 71
Florida
Do you think in my situation that my copper water line is bonded properly? The unistrut which carries the copper water line is bolted to the building steel. The building steel is bonded to the egc. Would that be a sufficient bond? In the building I'm working on the plumber has changed over from pvc to copper all over the place. So, I'm just tring to figure out everywhere I need to run a bond wire. {It's a industrial cemical building}

2017 / 2014 NEC & Related Books and Study Guides
Re: Bonding water pipe #96172
11/07/05 11:19 AM
11/07/05 11:19 AM
R
raider1  Offline
Member
Joined: Jul 2005
Posts: 46
north logan, utah, US
Take a look a 205.104 NEC 2005.

I think that to be code compliant you would need to use a water pipe clamp and install a bonding jumper to the building steel installed in accordance with 250.64(A)(B)(E)

JMHO, Chris

Re: Bonding water pipe #96173
11/08/05 05:13 PM
11/08/05 05:13 PM
T
Tesla  Offline
Member
Joined: Jun 2004
Posts: 1,273
Sacramento, CA
That plumber better have his work cleared by the engineers. Many, many chemicals will tear up copper. I suspect that is why the original installation was in plastic.

Don't be too surprised if the plumber gets spanked. Who approved this dramatic change?


Tesla
Re: Bonding water pipe #96174
11/08/05 06:33 PM
11/08/05 06:33 PM
S
sid123456  Offline OP
Member
Joined: Jan 2005
Posts: 71
Florida
He passed his final inspection. I asked the same question. Why am I using pvc coated ridged when he is using copper. It's water treatment cemicals, very corrosive.

Re: Bonding water pipe #96175
11/08/05 08:45 PM
11/08/05 08:45 PM
C
caselec  Offline
Member
Joined: Apr 2002
Posts: 558
San Jose, CA
The copper water lines should have isolation straps at the strut so there is no metal to metal contact. If the copper lines are held with standard strut clamps both the plumber and the plumbing inspector are not very bright.

Curt


Curt Swartz
Re: Bonding water pipe #96176
11/19/05 12:17 PM
11/19/05 12:17 PM
P
Paul O'Connell  Offline
Member
Joined: Jul 2005
Posts: 56
Allen Park, Mi. USA
Two key words in bonding requirements.

1. Perminent.
2. Approved fittings.

Re: Bonding water pipe #96177
11/19/05 03:14 PM
11/19/05 03:14 PM
E
earlydean  Offline
Member
Joined: Dec 2003
Posts: 751
Griswold, CT, USA
It may be that the particular chemicals used do not react with copper, but do react with steel. Or, the copper pipes may be slated to be painted or covered later. The inspector may not be aware of the corrosive qualities, but the designing engineer should.

The code (250.104(A)(1)) requires water piping SYSTEMS to be bonded to the grounding electrode system, either to the GEC, to the service neutral bus or to a grounding electrode used (such as building steel)

If you have isolated sections of water pipe, you may not have to bond all of them together. This call, as to when an isolated pipe becomes long enough to be considered a system, lies with the AHJ. To be safe bond them all together, and to the grounding system.

Like Paul said, make your connections permanent and use approved fittings designed for the purpose and conditions of use.


Earl

Featured:

2017 Master Electrician Exam Preparation Combos
2017 NEC Electrician
Exam Prep Combos:
Master / Journeyman

 

Member Spotlight
Attic Rat
Attic Rat
Bergen Co.,N.J. USA
Posts: 524
Joined: December 2003
Show All Member Profiles 
Top Posters(30 Days)
Admin 9
Popular Topics(Views)
244,092 Are you busy
181,135 Re: Forum
171,327 Need opinion
Powered by UBB.threads™ PHP Forum Software 7.6.1
(Release build 20180101)
Page Time: 0.021s Queries: 14 (0.004s) Memory: 0.9837 MB (Peak: 1.1369 MB) Zlib enabled. Server Time: 2018-02-25 23:36:33 UTC