Conductor Derating 2 #95979
10/27/05 11:11 AM
10/27/05 11:11 AM
C
cgw  Offline OP
Member
Joined: Jul 2004
Posts: 133
Rochester NY
Thsi topic is being discussed in two other threads but here is a different question.
Assume 10 120V circuits each with their own neutral. #12 all in one conduit to a juction box with one ground wire and a ground bus in the junction box. Separate MC from there to the devices, lighting etc.
50% of 25A is 12.5 amps. Does that mean that the branch circuit breaker needs to be less than 12.5 amp? Or just that the connected load can not exceed 12.5 amps?

2017 / 2014 NEC & Related Books and Study Guides
Re: Conductor Derating 2 #95980
10/27/05 11:28 AM
10/27/05 11:28 AM
W
winnie  Offline
Member
Joined: Sep 2003
Posts: 649
boston, ma
The load on each circuit would need to be less than 12.5A, but you could use the next larger standard breaker, eg. a 15A breaker.

Note that for derating based upon number of conductors in a conduit, you get to work from the temperature rating of the wire, even if it is higher than that of the terminations. So you would probably use THHN 90C wire, with an ampacity of 30A, 15A after derating with a 15A breaker.

-Jon

Re: Conductor Derating 2 #95981
10/27/05 12:13 PM
10/27/05 12:13 PM
R
resqcapt19  Offline
Member
Joined: Nov 2000
Posts: 2,148
IL
Quote
The load on each circuit would need to be less than 12.5A, but you could use the next larger standard breaker, eg. a 15A breaker.

Not if the circuit supplies a multioutlet branch circuit supplying receptacles for cord-and-plug-connected portable loads.
See 240.4(B)(1).
Don


Don(resqcapt19)
Re: Conductor Derating 2 #95982
10/27/05 03:38 PM
10/27/05 03:38 PM
G
George Little  Offline
Member
Joined: Jan 2004
Posts: 1,489
Michigan USA
I agree Don, if the circuits are feeding receptacles you looking at 10a circuit breakers.


George Little
Re: Conductor Derating 2 #95983
10/27/05 08:29 PM
10/27/05 08:29 PM
C
cgw  Offline OP
Member
Joined: Jul 2004
Posts: 133
Rochester NY
OK, so for the receptacle circuits we can not go to the next higher size circuit breaker.
But, if the wire is 90C we can use 30 amp which means 15 amp and a 15 amp receptacle?
(regardless of the termination rating?)

Re: Conductor Derating 2 #95984
10/27/05 09:36 PM
10/27/05 09:36 PM
G
George Little  Offline
Member
Joined: Jan 2004
Posts: 1,489
Michigan USA
If you have a 90° wire (THHN) #12 AWG using it in a ambient of 86° damp or dry location and derate to 15a due to raceway fill, you could feed 15 receptacles and have a 15a overcurrent device protecting it.


George Little

Featured:

2017 Master Electrician Exam Preparation Combos
2017 NEC Electrician
Exam Prep Combos:
Master / Journeyman

 

Member Spotlight
mxslick
mxslick
Atomic City, ID USA
Posts: 803
Joined: October 2004
Show All Member Profiles 
Top Posters(30 Days)
Admin 8
Popular Topics(Views)
251,518 Are you busy
188,690 Re: Forum
178,391 Need opinion
Powered by UBB.threads™ PHP Forum Software 7.6.1
(Release build 20180101)
Page Time: 0.026s Queries: 14 (0.005s) Memory: 0.9760 MB (Peak: 1.1228 MB) Zlib enabled. Server Time: 2018-11-17 00:27:00 UTC