0 members (), 150 guests, and 35 robots.
#95886 10/17/05 11:12 AM
is it permissable to run a curcuit overhead from a residental home to a garage?
Workgear for Electricians
#95887 10/17/05 12:26 PM
See article 225
Mike
#95888 10/17/05 02:16 PM
Should also look at Article 396 which tells us, Yes if it's a factory assembly.
George Little
#95889 10/17/05 04:36 PM
George, why only a factory assembly 396.2(2)?
#95890 10/17/05 05:15 PM
so the way i read the code is it is allowed if i use triplex and maintain my clearances.
#95891 10/17/05 05:50 PM
Kinda a suggestion that if he is using a cable method to look in each Article called out in T. 396.10(A) but if it's single strands of wire as identified in T. 310.3 or T. 310.6 he would not be able to comply with the (B) part of 396.10 and not be able to use it in residential. And, Yes tom triplex probably would be the best approach. IMHO
George Little
#95892 10/17/05 06:34 PM
thank's for the info guys
#95893 10/17/05 06:37 PM
Why not UF cable on a messenger?
#95894 11/09/05 02:27 PM
If the circuit is 120/240 and there is any chance of a present or future metallic connection between the two buildings you will want to use quadplex.
Tom Horne
Tom Horne
#95895 11/09/05 02:32 PM
In My Unhumble Opinion (IMUhO) UF on a messenger makes one ugly installation.
Tom Horne
Tom Horne