ECN Electrical Forum - Discussion Forums for Electricians, Inspectors and Related Professionals
ECN Shout Chat
Shout Box
Recent Posts
Changing a Bulb
by mbhydro. 07/21/18 05:57 PM
Opinions & comments
by HotLine1. 07/21/18 04:44 PM
Tray cable?
by gfretwell. 07/11/18 10:18 PM
Eaton Heavy Duty 30A and 60A Safety Switches
by Admin. 07/11/18 09:49 PM
ORTOVOX Recalls Avalanche Transceivers
by Admin. 07/11/18 09:44 PM
New in the Gallery:
Plug terminals
Housebilding DIY wiring
Who's Online Now
0 registered members (), 26 guests, and 17 spiders.
Key: Admin, Global Mod, Mod
Previous Thread
Next Thread
Print Thread
Rate Thread
Two buildings from a remote service #95720
09/29/05 11:23 PM
09/29/05 11:23 PM
B
BigB  Offline OP
Member
Joined: Mar 2004
Posts: 725
Tucson, AZ USA
I have a customer with a pole mounted 400 amp service. From the meter enclosure, a 400 amp disco is fed thru a gutter. This is all grouped on a board at the pole. From the disco there are 3 500MCM which go underground about 100 feet to the main residence, where there is a 150A disco and MDP. Now they are building a shop which will have 100 amps run to it, also from the pole mounted service. The shop will probably have metallic paths to the main residence, but not to the pole mounted service.
Question is, 3 wire or 4 to the shop? I feel 4 are required since in the event of an open neutral, the current would attempt to return thru the metal path to the main house where it would find the neutral at the bond there. Also, if the main house experienced an open neutral, the current would return thru the metal path to the shop then on to the service. I am 99% sure on this but would like some confirmation.

(P.S. The metallic path would be phone/cable. The water will be PVC and no gas)

2017 / 2014 NEC & Related Books and Study Guides
Re: Two buildings from a remote service #95721
09/30/05 03:03 PM
09/30/05 03:03 PM
E
earlydean  Offline
Member
Joined: Dec 2003
Posts: 751
Griswold, CT, USA
Check out 250.32(B). It gives you two options: with or without an equip. ground.
Option (2) is without the equipment grounding conductor, and the rules for this option include: "there are no continuous metallic paths bonded to the grounding system in each building or structure involved".
Sounds like you are right.
The reasoning isn't so much for the eventuality of an open neutral, but more for the fact of a definite parallel path with the grounded conductor, which is to be avioded. How would you like to disconnect the shield on your cable TV, and pull an arc? Or, work on the plumbing, and get rapped?


Earl
Re: Two buildings from a remote service #95722
09/30/05 09:44 PM
09/30/05 09:44 PM
G
gfretwell  Offline

Member
Joined: Jul 2004
Posts: 9,242
Estero,Fl,usa
If he feeds the house and the shop from a maypole and then closes the loop with a wire between the house and the shop he is going to have objectionable currents, whether he does 3 or 4 wire. I would have the cable and phone companies set dmarks at both buildings and let them deal with stopping the loop current. At that point you don't have a metalic path.


Greg Fretwell
Re: Two buildings from a remote service #95723
10/04/05 08:42 PM
10/04/05 08:42 PM
M
mhulbert  Offline
Member
Joined: Oct 2004
Posts: 132
Anaheim, CA USA
Even with demarcs, you are going to have metallic paths! If both buildings have the smae phone line - now or in the future- they will have a common path. Cable will always have a common path, that's also bonded to ground at each building via the shield.
The electrons don't care if they are going through a demarc or not.

4 wire is the only way to go with something like this. Even if you can prove there are no mettalic paths now, is the gas man going to repull wires when they or a future resident install gas down the road?

Re: Two buildings from a remote service #95724
10/04/05 10:02 PM
10/04/05 10:02 PM
B
BigB  Offline OP
Member
Joined: Mar 2004
Posts: 725
Tucson, AZ USA
Thanks Guys.......4 wire it is

Re: Two buildings from a remote service #95725
10/05/05 01:45 AM
10/05/05 01:45 AM
G
gfretwell  Offline

Member
Joined: Jul 2004
Posts: 9,242
Estero,Fl,usa
If you close the loop between buildings it is worse that the "metalic path" problem. You have made a loop and eddy currents will flow. Lightning will fry everything on that loop.
The Dmark will surge protect these on the phone (there is no grounded phone conductor). I am not sure how they accomplish it with cable.
I have to believe there is some kind of isolation.


Greg Fretwell

Featured:

2017 Master Electrician Exam Preparation Combos
2017 NEC Electrician
Exam Prep Combos:
Master / Journeyman

 

Member Spotlight
lil suzi
lil suzi
Midwest
Posts: 57
Joined: August 2003
Show All Member Profiles 
Top Posters(30 Days)
Admin 5
Popular Topics(Views)
248,161 Are you busy
185,637 Re: Forum
175,005 Need opinion
Powered by UBB.threads™ PHP Forum Software 7.6.1
(Release build 20180101)
Page Time: 0.020s Queries: 14 (0.004s) Memory: 0.9777 MB (Peak: 1.1232 MB) Zlib enabled. Server Time: 2018-07-22 21:48:00 UTC