Does anyone have any information on the use of reducing washers?
George Little
|
|
|
|
Joined: Jan 2003
Posts: 4,391
Moderator
|
UL White Book OUTLET BUSHINGS AND FITTINGS (QCRV) GROUNDING Metal reducing washers are considered suitable for grounding for use in circuits over and under 250 V and where installed in accordance with ANSI/NFPA 70, ‘‘National Electrical Code.’’ That's all I have except they make big holes small.
Bob Badger Construction & Maintenance Electrician Massachusetts
|
|
|
|
Joined: Jan 2004
Posts: 1,507
OP
Member
|
Thanks Bob- That's what I needed.
George Little
|
|
|
|
Joined: Nov 2000
Posts: 2,148
Member
|
That information really makes me question the technical expertise of UL. Don
Don(resqcapt19)
|
|
|
|
Joined: Jan 2003
Posts: 4,391
Moderator
|
Don I think the problem is the difference between test conditions and real life.
I have no doubt you or I could make reducing washers carry fault current if we used a wire brush to remove all paint from the enclosure and tightened the lock nuts decently.
However I know I see reducing washers all the time that are up against paint and loose.
I think an inspector could cite 250.12 Clean Surfaces almost every time.
Personally I dislike everything about reducing washers.
Bob Badger Construction & Maintenance Electrician Massachusetts
|
|
|
|
Joined: Aug 2003
Posts: 1,374
Moderator
|
I discussed this matter with the UL representative of CMP 5 (Article 250). He was surprised as well, but looking at the listing standard, it appears as though under test conditions reducing washers that are listed are capable of carrying a tremendous amount of fault current. I don't recall the exat test now, but it was several thousand amps for a substantial duration.
Ryan Jackson, Salt Lake City
|
|
|
|
Joined: Nov 2000
Posts: 2,148
Member
|
I'm sorry, but if the test conditions do not represent a real world installation, the results are worthless. Don
Don(resqcapt19)
|
|
|
|
Joined: Jul 2004
Posts: 9,928 Likes: 34
Member
|
I vote with Bob. Reducing washers keep the connector from falling out but I would use a bonding nut if I wanted to make a secure grounding connection.
Greg Fretwell
|
|
|
|
Joined: Jun 2004
Posts: 1,273
Member
|
Reducers -- gotta hate 'em....
Every time I see them it's a hack job.
I particularly dislike reducers used at NEMA3R disconnects where the installer is shrinking back from a 1 inch KO goof.
Tesla
|
|
|
|
Joined: Jan 2005
Posts: 109
Member
|
I hate RE plates. I would rather screw a plate in the can and make sure there is a ground wire. I have had inspectors fail an installation; he wanted reducing washers; I had bolted a cover plate to the top of the box and had a grounding bushing and ground wire in the EMT. My way was better and I proved it to him with a megger. He made me change it to pass inspection. Still scratching my head Rod.
|
|
|