1 members (HotLine1), 150 guests, and 15 robots.
#95454 09/14/05 01:42 AM
where in nec does it say you have use a pvc connector at the end of a pipe in the ground fed with uf?
is this a wives tale. 300.4 apply?
and the wire is smaller then #4 so the only bushing requirement doesnt apply.
i always do it(trained this way) but wonder if i have to.
h20
#95455 09/14/05 05:09 AM
How about 300.5 (H) Bushing. A bushing, or terminal fitting, with an integral bushed opening shall be used at the end of a conduit or other raceway that terminates underground where the conductors or cables emerge as a direct burial wiring method. A seal incorporating the physical protection characteristics of a bushing shall be permitted to be used in lieu of a bushing.
Could this be it?
Mike
#95456 09/14/05 03:36 PM
this 300.5 must be it....
thanks
h20
#95457 09/14/05 04:37 PM
Also 300.15(C)
320,019 Are you busy
245,207 Re: Forum
228,636 Need opinion
