Posted By: watersparkfalls bushing - 09/14/05 05:42 AM
where in nec does it say you have use a pvc connector at the end of a pipe in the ground fed with uf?

is this a wives tale. 300.4 apply?
and the wire is smaller then #4 so the only bushing requirement doesnt apply.

i always do it(trained this way) but wonder if i have to.

h20
Posted By: jw electric Re: bushing - 09/14/05 09:09 AM
How about 300.5 (H) Bushing. A bushing, or terminal fitting, with an integral bushed opening shall be used at the end of a conduit or other raceway that terminates underground where the conductors or cables emerge as a direct burial wiring method. A seal incorporating the physical protection characteristics of a bushing shall be permitted to be used in lieu of a bushing.

Could this be it?
[Linked Image]
Posted By: watersparkfalls Re: bushing - 09/14/05 07:36 PM
this 300.5 must be it....
thanks

h20
Posted By: eprice Re: bushing - 09/14/05 08:37 PM
Also 300.15(C)