#95205 09/04/05 03:12 PM
gserve Offline OP
Where in the 2005 code does it state that romex cannot directly feed the dishwasher(romex in wall wired directly to the dishwasher junction box)or is it just a protection issue and needs to be sleeved in flex from wall to dishwasher JB?
Work Gear for Electricians and the Trades
Workgear for Electricians
#95206 09/04/05 06:12 PM
The NEC doesn't prohibit connecting directly with NM cable but the majority of the dishwashers I inspect are cord and cap connected for three good reasons.
1. It's easier to connect a cord before they install the dishwasher and have a receptacle in the sink base cabinet to plug it into. Cord to be 3-4 feet long max. See 422.16(B)(2)
2. You now have no issues with having a disconnect at the appliance.
3. The plumber now doesn't have to deal with a hard wired connection when he/she has to pull the unit out for servicing.
George Little
#95207 09/04/05 09:27 PM
How do you resolve "closely follow building finish" and "secured ... within 300 mm (12 in.) of every cabinet, box, or fitting."?
#95208 09/04/05 10:20 PM
That's reason number 4. to use a cord and cap ::
George Little