#95198 - 09/04/05 09:37 AM Kitchen recepts  
SparksNmore  Offline
Member
Joined: May 2005
Posts: 16
KC KS
Here's a question copied from another message forum board (non electrical)

As forum boards usually go, he got several wrong replies from DIY's

Quote

I'm a L.V.P (Low Voltage Puke to the uneducated), and I'm not up on some things.

We're remodeling the kitchen, and the cabinet installers are coming Tuesday. I'd like to get wiring roughed in this weekend before they bury me in new millwork.

Question about kitchen branch circuits - what I'm aware of:
Current code requires a minimum of 2) 20A circuits for a kitchen.
A countertop of more than 12" horiz. run requires an outlet accessable to it.
Within the "run" of the countertop, no more than a 24" reach to an outlet.

What I'd like to do is install duplex recepticles at the required spacing, and split them (breaking the connector tabs between outlets - hot side). Each 1/2 would have it's own feed from each of the 2) 20A circuits.

My question is:
Would I have to run separate neutrals to each 1/2 of the outlet, or just upsize the guage of the neutral and keep them "commoned" (they go back to the same buss bar anyway)??

Help needed!



What do y'all think?


2017 / 2014 NEC & Related Books and Study Guides

#95199 - 09/04/05 11:28 AM Re: Kitchen recepts  
gfretwell  Offline


Member
Joined: Jul 2004
Posts: 9,142
Estero,Fl,usa
The GFCI keeps that idea from working.


Greg Fretwell

#95200 - 09/04/05 06:45 PM Re: Kitchen recepts  
e57  Offline
Member
Joined: May 2003
Posts: 2,876
S.F.,CA USA
"Help needed!" - No kidding....

I guess it could be done with a 2-pole GFI CB with a single neutral, and split only the hot, but why?

So I assume the correct reply was hire a qualified electrician?


Mark Heller
"Well - I oughta....." -Jackie Gleason

#95201 - 09/04/05 09:54 PM Re: Kitchen recepts  
SparksNmore  Offline
Member
Joined: May 2005
Posts: 16
KC KS
Final answer was:

Quote

Do NOT do it with a 12-3 or any other shared nuetral way.

This will NOT work. I hope you haven't done it already.

All kitchen recepticles need to be GFCI protected by NEC code.

If you use a shared nuetral on a GFCI, as soon as you use one half of the recepticle you will trip both GFCI's. The unbalance of current on the nuetral will be read by both GFCI's and will trip them. You will never be able to use the recepticles.

I am a master electrician, and have had to fish lots of wire into remodeled kitchens where home owners tried this. It will NOT work.

If you are going to do it, use 2 12-2 wires and break both tabs on each recepticle. As stated you will then have to put the two circuits on a 2 pull breaker. Reason being that you have to turn off both circuits to work on one recepticle.

If you are going to do this, do NOT wire your refridgerator into either of these circuits. If one trips they both trip and you do not want that surprise after a vacation or long weekend. Also when pulling the wire, make sure you don't GFCI protect the refridgerator, yet another surprise you don't want.

If you have any other questions feel free to ask.



#95202 - 09/05/05 02:46 PM Re: Kitchen recepts  
ShockMe77  Offline
Member
Joined: Jun 2005
Posts: 821
Rahway, New Jersey
Why do homeowners insist on doing it the least practical way? Is it to impress their neighbors and friends? I dunno.

This dope needs to run 12-3 NM and jump out with 12-2 to another box. Also, be sure to splice the neutral through so it doesn't accidentially send 160 volts to the microwave and 50 volts to a coffee maker. This prevents the "unbalanced" load in the neutral wire from ruining your kitchen appliances.


#95203 - 09/05/05 03:21 PM Re: Kitchen recepts  
gfretwell  Offline


Member
Joined: Jul 2004
Posts: 9,142
Estero,Fl,usa
This may be the Canadian influence. That is/was the standard way to wire kitchen receptacles up there.


Greg Fretwell

#95204 - 09/05/05 03:42 PM Re: Kitchen recepts  
Redsy  Offline
Member
Joined: Mar 2001
Posts: 2,056
Bucks County PA
What about box fill?
9 X 2.25 = 20.25 (12/3 NM X 2)
11 X 2.25 = 24.75 (12/2 X 4)




[This message has been edited by Redsy (edited 09-05-2005).]



Member Spotlight
Samurai
Samurai
Fl.
Posts: 46
Joined: May 2007
Show All Member Profiles 
Featured:

2017 Master Electrician Exam Preparation Combos
2017 NEC Electrician
Exam Prep Combos:
Master / Journeyman

 

Shout Box
Powered by UBB.threads™ PHP Forum Software 7.6.0
Page Time: 0.015s Queries: 14 (0.003s) Memory: 0.7865 MB (Peak: 0.9363 MB) Zlib enabled. Server Time: 2017-12-14 07:54:33 UTC