ECN Electrical Forum - Discussion Forums for Electricians, Inspectors and Related Professionals
ECN Shout Chat
Top Posters(30 Days)
dsk 13
Admin 8
doc 3
Recent Posts
Bathroom electrical
by doc. 08/19/17 06:53 AM
electircal ageing test on IPC
by SIAME. 08/15/17 02:43 AM
electrical aging test on IPC
by gfretwell. 08/15/17 12:27 AM
"Line level" audio on Cat 5?
by gfretwell. 08/08/17 10:39 PM
Fire alarm phone lines and color coding
by gfretwell. 08/08/17 10:26 PM
New in the Gallery:
Gallery Test
Popular Topics(Views)
239,976 Are you busy
175,569 Re: Forum
167,817 Need opinion
Who's Online Now
0 registered members (), 58 guests, and 8 spiders.
Key: Admin, Global Mod, Mod
Previous Thread
Next Thread
Print Thread
Rate This Thread
#95137 - 09/01/05 01:06 AM EMT Support  
jtedson  Offline
Junior Member
Joined: May 2004
Posts: 1
Federal Way,WA,USA
There is a little debate at work about the wording of the code on this issue. In 358.30(A) it says "other tubing terminations" shall be securly fastened within 3 ft. One of my fellow workers insists this means every coupling. While most of agree this is good practice to secure the pipe close to a coupling if practical, we feel the code is referring to a connector in this instance. Any feedback on this would be great. Thank you in advance.


2017 / 2014 NEC & Related Books and Study Guides

#95138 - 09/01/05 01:30 AM Re: EMT Support  
watersparkfalls  Offline
Member
Joined: Mar 2005
Posts: 216
Washington...Not DC
358.30(A) securely fastened. emt shall be securely fastened in place at least every 3 m (10 ft.) in assition, each emt run between termination points shall be securely fastened within 900 mm (3 ft.) of each outlet box, junction, box, device box, cabinet, conduit body, or other tubing termination.

ok i think they are reading to hard into "other" forgetting the word "termination" within 3 ft of termination and certainly couplings are not terminating but merely continuing until one does terminate.

imho

h20


#95139 - 09/01/05 06:14 AM Re: EMT Support  
Roger  Offline
Member
Joined: May 2002
Posts: 1,716
N.C.
I agree with h20, a coupling is not a termination.

If couplings were to be included, the word "coupling" could have been in the article.

Check the link below for anothers opinion.
http://www.mikeholt.com/reprint_request.php?url=http://www.mikeholt.com/graphics/348-13.gif

Roger


#95140 - 09/03/05 07:53 AM Re: EMT Support  
iwire  Offline
Moderator
Joined: Jan 2003
Posts: 4,391
North Attleboro, MA USA
I had this same misconception and it stems from the fact the code was changed.

The section used to actually say "fitting" a coupling is definitely a fitting.

1990 NEC
Quote
348-12 Supports. Electrical metallic tubing shall be installed as a complete system as provided in Article 300 and shall be securely fastened in place at least every 10 feet (3.05m) and within feet (914mm) of each outlet box, junction box, cabinet or fitting.


This may or not be the same wording in the 1993 NEC I do not have a 1993 NEC available.

Personally I find the change to be in the wrong direction, IMO a support should be required within 3' of a EMT coupling.



[This message has been edited by iwire (edited 09-03-2005).]


Bob Badger
Construction & Maintenance Electrician
Massachusetts


Member Spotlight
Samurai
Samurai
Fl.
Posts: 46
Joined: May 2007
Show All Member Profiles 
Featured:

2017 Master Electrician Exam Preparation Combos
2017 NEC Electrician
Exam Prep Combos:
Master / Journeyman

 

Shout Box
Powered by UBB.threads™ PHP Forum Software 7.6.0
Page Time: 0.011s Queries: 14 (0.002s) Memory: 0.7611 MB (Peak: 0.8946 MB) Zlib enabled. Server Time: 2017-08-20 08:06:21 UTC