Damaged outlets #94916
08/19/05 08:41 AM
08/19/05 08:41 AM
G
ghill  Offline OP
Junior Member
Joined: Aug 2005
Posts: 3
Clarksville, TN
My company maintains over 4000 military homes on a prominanate installation and many others on other installations.

Recently some housing inspectors that have no electrical training have decided that if an occupant wiggles their electrical plug when they are extracting it from an outlet and breaks the tiny piece of plastic that is immediately adjacent to the grounding slot on the outlet that the outlet must be replaced. The damage is extremely minor and is not normally even noticed unless one examines it closely. I'm hoping that many of you have seen just how small this damage is and can help me as I struggle with this issue. The NEC Code that probably applies is:

NEC 110.12 (C), page 70-34, which states the following:

"Integrity of Electrical Equipment and Connection.
Internal parts of electrical equipment, including busbars, wiring terminals, insulators, and other surfaces, shall not be damaged or contaminated by foreign materials such as paint, plaster, cleaners, abrasives, or corrosive residues. There shall be no damaged parts that may adversely affect safe operations or mechanical strength of the equipment such s parts that are broken; bent; cut; or deteriorated by corrosion, chemical action, or overheating."

As it pertains to the first sentence, this damage is not internal, and as it pertains to the last sentence it does not adversely effect safe operations or mechanical strength. In that it poses no safety hazard I submit that the replacement of these outlets, often new ones, is unnessary and the money spent for this could be better spent on other safety issues. I would appreciate your thoughts.

2017 / 2014 NEC & Related Books and Study Guides
Re: Damaged outlets #94917
08/19/05 09:27 AM
08/19/05 09:27 AM
L
Larry Fine  Offline
Member
Joined: Feb 2005
Posts: 693
Richmond, VA
My first thoughts agree with yours: there is no danger.

My second thoughts are that, if I'm getting paid, no problem.


Larry Fine
Fine Electric Co.
fineelectricco.com
Re: Damaged outlets #94918
08/19/05 08:34 PM
08/19/05 08:34 PM
W
William Runkle  Offline
Member
Joined: Feb 2003
Posts: 27
Dowagiac, Michigan U.S.A.
I agree with Larry. So who do you charge for this? And is it like a Thousand Dollar toliet seat cost since it is a military complex possible big bucks and any questions blame the inspectors.


William Runkle
Re: Damaged outlets #94919
08/20/05 01:21 PM
08/20/05 01:21 PM
L
luckyshadow  Offline
Member
Joined: Jan 2005
Posts: 315
Maryland USA
I agree there is no real danger. I might even find one like that in my house.
I can see how this could become a "sore spot" for you if your company has a maintenance agreement and is charging a flat out yearly price to handle such minor things. On the other hand if you are able to charge for them why not wait until you have a days worth of work at any one particular base and go to it ?

Re: Damaged outlets #94920
08/20/05 05:18 PM
08/20/05 05:18 PM
J
jes  Offline
Member
Joined: Jul 2002
Posts: 103
CT
One upside to this is that there is a system of sorts to replace receptacles. You may not see other issues that may exist hidden in the device or related to the circuit connections. For example loose connections or poor tension. I would also expect the newer receptacles to be a bit less susceptable to the damage you are referring to. Do you perform any kind of test on the finished replacement?

Re: Damaged outlets #94921
08/29/05 09:02 AM
08/29/05 09:02 AM
G
ghill  Offline OP
Junior Member
Joined: Aug 2005
Posts: 3
Clarksville, TN
Thanks to all for your imput. I was sure hoping that Joe Tedesco would weigh back in on this one also, Joe are you out there?

Re: Damaged outlets #94922
08/29/05 04:56 PM
08/29/05 04:56 PM
L
Larry Fine  Offline
Member
Joined: Feb 2005
Posts: 693
Richmond, VA
While waiting for Joe to chiime in, I'd like to add a piece of advice:

As long as you're replacing the old receptacles anyway, and unless you're going to throw the main breaker, use a piece of wire to short each circuit at every receptacle; don't assume anything!

On a similar job in a house, we found that the center bedroom's receptacles were being fed by three different circuits! The house was wired "up-n-down"; labeling the panel was an excercise in itself.

Edited for sentence structure. (Yes, it was worse before!)

[This message has been edited by Larry Fine (edited 08-29-2005).]


Larry Fine
Fine Electric Co.
fineelectricco.com
Re: Damaged outlets #94923
08/29/05 05:16 PM
08/29/05 05:16 PM
G
George Little  Offline
Member
Joined: Jan 2004
Posts: 1,489
Michigan USA
Quote
As long as you're replacing the old receptacles anyway, and unless you're going to throw the main breaker, use a piece of wire to short each circuit at every receptacle; don't assume anything!


Larry would you mind if I paid for some insurance on you? I'll make me the beneficiary.

My advice, don't short out circuits to trip the overcurrent device. Definitely a bad work habit.


George Little
Re: Damaged outlets #94924
08/29/05 05:51 PM
08/29/05 05:51 PM
R
Roger  Offline
Member
Joined: May 2002
Posts: 1,716
N.C.
Larry, I am with George. Besides the obvious dangers, this can cause hidden conductor damage also, especially if the trip is not intantaneous.

Roger

[This message has been edited by Roger (edited 08-29-2005).]

Re: Damaged outlets #94925
08/29/05 06:31 PM
08/29/05 06:31 PM
Joe Tedesco  Offline
Member
Joined: Oct 2000
Posts: 2,749
Boston, Massachusetts USA
I am here and await the response from the people you have criticized for attempting to use a rule discussed in a class they recently attended.

Please settle this issue with them, and let's see and hear the rest of the story.


Joe Tedesco, NEC Consultant
Page 1 of 4 1 2 3 4

Featured:

2017 Master Electrician Exam Preparation Combos
2017 NEC Electrician
Exam Prep Combos:
Master / Journeyman

 

Member Spotlight
mxslick
mxslick
Atomic City, ID USA
Posts: 803
Joined: October 2004
Show All Member Profiles 
Top Posters(30 Days)
Admin 8
Popular Topics(Views)
251,487 Are you busy
188,678 Re: Forum
178,379 Need opinion
Powered by UBB.threads™ PHP Forum Software 7.6.1
(Release build 20180101)
Page Time: 0.027s Queries: 15 (0.005s) Memory: 1.0284 MB (Peak: 1.2028 MB) Zlib enabled. Server Time: 2018-11-16 01:37:51 UTC