#94719 07/06/05 01:41 AM
Joined: Mar 2005
Posts: 240
Member
i want to know if anybody can help me calculate if i can put a 1/2 HP disposer motor and a dishwasher that draws a nameplate or 9.1 amps on a 20 amp circuit.

Horizontal Ad
#94720 07/06/05 12:39 PM
Joined: Jul 2004
Posts: 10,022
Likes: 37
G
Member
Nominal FLA on a 1/2 HP motor is 9.8a (plus 25%) added to 9.1a seems to be too much for a multiple motor load.
If you are cord and plug connected they each do represent less than 50% of circuit ampacity so it might be "hold your nose" legal. I have seen this go both ways but the preferable solution is a multiwire circuit with 2 phases feeding the duplex.


Greg Fretwell
#94721 07/07/05 02:12 AM
Joined: Mar 2005
Posts: 240
Member
thanks gf i just wondered if possible...
could you elaborate on the 50% since cord connected dishwashers are feasible and do provide disconnecting means for motor.

h2o

#94722 07/07/05 12:39 PM
Joined: Jul 2004
Posts: 10,022
Likes: 37
G
Member
It all gets down to how you read
210.23(A)(2) Utilization Equipment Fastened in Place. The total rating of utilization equipment fastened in place, other than luminaires (lighting fixtures), shall not exceed 50 percent of the branch-circuit ampere rating where lighting units, cord-and-plug-connected utilization equipment not fastened in place, or both, are also supplied.

Most inspectors would say all fixed in place equipment must be less than 50% but I have seen this stretched to say any one piece can't exceed 50%, particularly on an intermittant load like a disposal.
Vote me for "all".


Greg Fretwell
#94723 07/07/05 10:03 PM
Joined: Jan 2005
Posts: 5,476
Likes: 3
Cat Servant
Member
One caution here....look at the FLA on the disposal, and not the "horsepower" rating. I have seen a lot of inflated "horsepower ratings" over the years.

#94724 07/12/05 09:46 PM
Joined: Feb 2005
Posts: 693
L
Member
"...lighting units (or) cord-and-plug-connected utilization equipment not fastened in place..."

Neither describe either a dishwasher or a disposer, so 210.23(A)(2) doesn't apply.

I routinely place both of these on a 20-amp circuit. A disposer is probably the epitome of an intermittent load.


Larry Fine
Fine Electric Co.
fineelectricco.com
#94725 07/12/05 09:55 PM
Joined: Feb 2005
Posts: 693
L
Member
According to Insinkerator specs, the 1/2HP Badger 5 has an average current draw of 6.9A.
http://www.insinkerator.com/pdf/badger5.PDF


Larry Fine
Fine Electric Co.
fineelectricco.com
Horizontal Ad
#94726 08/10/05 09:27 AM
Joined: Apr 2005
Posts: 73
D
Member
Good subject. I have been told that they make a 3 way switch that can be used in these applications. One position for dishwasher and other for disposal. Now having said that I personally have not seen one. Do they make them?

#94727 08/10/05 10:23 AM
Joined: Oct 2004
Posts: 135
B
Member
Any 3-way rated for the load would work.

#94728 08/10/05 05:43 PM
Joined: Aug 2003
Posts: 1,374
R
Moderator
I am moving this to the NEC section.


Ryan Jackson,
Salt Lake City
#94729 08/10/05 06:01 PM
Joined: Jan 2005
Posts: 316
L
Member
I think what should be used is a single pole, double throw switch. on-off-on

#94730 08/10/05 07:36 PM
Joined: May 2003
Posts: 2,876
E
e57 Offline
Member
They do make an "Air Switch" that has two plugs on it that switches back and forth like a three way. Hit the switch, and the unit takes power supplied to a Hot water dispensor, and turns on the Disposal. Hit the switch again, same in reverse...

However, I wouldn't think of using it, or a 3-way switch like that for a Dish Washer. It would become a nusiance to the home owner to reset the DW cycle everytime the GB was used. And you would have the HO curse your name every time they remembered that you cheaped out and didn't run a circuit for the extra $25 dollars of material and minimal effort. (Not that 'they' would know that, but you would...)

Common practice to just run a 3-wire to the sink for the both as a give-in. Priced that way off the bat. That way you're covered if they up-grade the appliances after rough, or anytime in the future.


Mark Heller
"Well - I oughta....." -Jackie Gleason
#94731 08/10/05 09:57 PM
Joined: Apr 2002
Posts: 7,413
Likes: 9
Member
Guys:
Just a heads-up; check the nameplate on the DW. 9.1 amps total load; hmm....15 amp OCP
CHECK the nameplate before installing the CB,

GD's vary, 4.9 FLA, 8.25 FLA, etc.

Most guys around here run #12 to DW, 15 amp CB; #14 for disposal....H/R. Most DW are hard wired; disposals are probably a 50/50 mix.

John


John
#94732 08/14/05 06:21 PM
Joined: Jun 2004
Posts: 24
R
Member
Around here we just put the garbage disposal on one of the 2 required appliance circuits and the dishwasher usually gets its own 15 or 20 Amp circuit.It really works well-absolutely no callbacks!

#94733 08/14/05 07:41 PM
Joined: May 2003
Posts: 2,876
E
e57 Offline
Member
Rhino - No other outlets.... Means no GB/DW, etc. Refers and ignitors for rangetops are an exception and Din rm/ pantry plugs.

Quote
210.52(2) No Other Outlets. The two or more small-appliance branch circuits specified in 210.52(B)(1) shall have no other outlets.


Mark Heller
"Well - I oughta....." -Jackie Gleason
Page 1 of 2 1 2

Link Copied to Clipboard
Featured:

 Electrical
 Clearance

 *
 Tools
 *

 Books

 *

 Test Equipment

 

Advertisement:-Right
Member Spotlight
Bill Addiss
Bill Addiss
NY, USA
Posts: 4,158
Joined: October 2000
Top Posters(30 Days)
Trumpy 5
davey 1
Popular Topics(Views)
550,017 Are you busy
424,613 Re: Forum
395,994 Need opinion
New Page 2
Powered by UBB.threads™ PHP Forum Software 7.7.5