0 members (),
235
guests, and
21
robots. |
Key:
Admin,
Global Mod,
Mod
|
|
|
Joined: Mar 2005
Posts: 240
OP
Member
|
i want to know if anybody can help me calculate if i can put a 1/2 HP disposer motor and a dishwasher that draws a nameplate or 9.1 amps on a 20 amp circuit.
|
|
|
|
Joined: Jul 2004
Posts: 10,022 Likes: 37
Member
|
Nominal FLA on a 1/2 HP motor is 9.8a (plus 25%) added to 9.1a seems to be too much for a multiple motor load. If you are cord and plug connected they each do represent less than 50% of circuit ampacity so it might be "hold your nose" legal. I have seen this go both ways but the preferable solution is a multiwire circuit with 2 phases feeding the duplex.
Greg Fretwell
|
|
|
|
Joined: Mar 2005
Posts: 240
OP
Member
|
thanks gf i just wondered if possible... could you elaborate on the 50% since cord connected dishwashers are feasible and do provide disconnecting means for motor.
h2o
|
|
|
|
Joined: Jul 2004
Posts: 10,022 Likes: 37
Member
|
It all gets down to how you read 210.23(A)(2) Utilization Equipment Fastened in Place. The total rating of utilization equipment fastened in place, other than luminaires (lighting fixtures), shall not exceed 50 percent of the branch-circuit ampere rating where lighting units, cord-and-plug-connected utilization equipment not fastened in place, or both, are also supplied.
Most inspectors would say all fixed in place equipment must be less than 50% but I have seen this stretched to say any one piece can't exceed 50%, particularly on an intermittant load like a disposal. Vote me for "all".
Greg Fretwell
|
|
|
|
Joined: Jan 2005
Posts: 5,476 Likes: 3
Cat Servant Member
|
One caution here....look at the FLA on the disposal, and not the "horsepower" rating. I have seen a lot of inflated "horsepower ratings" over the years.
|
|
|
|
Joined: Feb 2005
Posts: 693
Member
|
"...lighting units (or) cord-and-plug-connected utilization equipment not fastened in place..."
Neither describe either a dishwasher or a disposer, so 210.23(A)(2) doesn't apply.
I routinely place both of these on a 20-amp circuit. A disposer is probably the epitome of an intermittent load.
Larry Fine Fine Electric Co. fineelectricco.com
|
|
|
|
Joined: Apr 2005
Posts: 73
Member
|
Good subject. I have been told that they make a 3 way switch that can be used in these applications. One position for dishwasher and other for disposal. Now having said that I personally have not seen one. Do they make them?
|
|
|
|
Joined: Oct 2004
Posts: 135
Member
|
Any 3-way rated for the load would work.
|
|
|
|
Joined: Aug 2003
Posts: 1,374
Moderator
|
I am moving this to the NEC section.
Ryan Jackson, Salt Lake City
|
|
|
|
Joined: Jan 2005
Posts: 316
Member
|
I think what should be used is a single pole, double throw switch. on-off-on
|
|
|
|
Joined: May 2003
Posts: 2,876
Member
|
They do make an "Air Switch" that has two plugs on it that switches back and forth like a three way. Hit the switch, and the unit takes power supplied to a Hot water dispensor, and turns on the Disposal. Hit the switch again, same in reverse...
However, I wouldn't think of using it, or a 3-way switch like that for a Dish Washer. It would become a nusiance to the home owner to reset the DW cycle everytime the GB was used. And you would have the HO curse your name every time they remembered that you cheaped out and didn't run a circuit for the extra $25 dollars of material and minimal effort. (Not that 'they' would know that, but you would...)
Common practice to just run a 3-wire to the sink for the both as a give-in. Priced that way off the bat. That way you're covered if they up-grade the appliances after rough, or anytime in the future.
Mark Heller "Well - I oughta....." -Jackie Gleason
|
|
|
|
Joined: Apr 2002
Posts: 7,413 Likes: 9
Member
|
Guys: Just a heads-up; check the nameplate on the DW. 9.1 amps total load; hmm....15 amp OCP CHECK the nameplate before installing the CB,
GD's vary, 4.9 FLA, 8.25 FLA, etc.
Most guys around here run #12 to DW, 15 amp CB; #14 for disposal....H/R. Most DW are hard wired; disposals are probably a 50/50 mix.
John
John
|
|
|
|
Joined: Jun 2004
Posts: 24
Member
|
Around here we just put the garbage disposal on one of the 2 required appliance circuits and the dishwasher usually gets its own 15 or 20 Amp circuit.It really works well-absolutely no callbacks!
|
|
|
|
Joined: May 2003
Posts: 2,876
Member
|
Rhino - No other outlets.... Means no GB/DW, etc. Refers and ignitors for rangetops are an exception and Din rm/ pantry plugs. 210.52(2) No Other Outlets. The two or more small-appliance branch circuits specified in 210.52(B)(1) shall have no other outlets.
Mark Heller "Well - I oughta....." -Jackie Gleason
|
|
|
Posts: 4,158
Joined: October 2000
|
|
|
|