ECN Electrical Forum - Discussion Forums for Electricians, Inspectors and Related Professionals
ECN Shout Chat
ShoutChat
Recent Posts
Safety at heights?
by gfretwell - 04/23/24 03:03 PM
Old low volt E10 sockets - supplier or alternative
by gfretwell - 04/21/24 11:20 AM
Do we need grounding?
by gfretwell - 04/06/24 08:32 PM
UL 508A SPACING
by tortuga - 03/30/24 07:39 PM
Increasing demand factors in residential
by tortuga - 03/28/24 05:57 PM
New in the Gallery:
This is a new one
This is a new one
by timmp, September 24
Few pics I found
Few pics I found
by timmp, August 15
Who's Online Now
0 members (), 228 guests, and 10 robots.
Key: Admin, Global Mod, Mod
Previous Thread
Next Thread
Print Thread
Rate Thread
Page 2 of 2 1 2
#94729 08/10/05 06:01 PM
Joined: Jan 2005
Posts: 316
L
Member
I think what should be used is a single pole, double throw switch. on-off-on

Stay up to Code with the Latest NEC:


>> 2023 NEC & Related Reference & Exam Prep
2023 NEC & Related Reference & Study Guides

Pass Your Exam the FIRST TIME with the Latest NEC & Exam Prep

>> 2020 NEC & Related Reference & Study Guides
 

#94730 08/10/05 07:36 PM
Joined: May 2003
Posts: 2,876
E
e57 Offline
Member
They do make an "Air Switch" that has two plugs on it that switches back and forth like a three way. Hit the switch, and the unit takes power supplied to a Hot water dispensor, and turns on the Disposal. Hit the switch again, same in reverse...

However, I wouldn't think of using it, or a 3-way switch like that for a Dish Washer. It would become a nusiance to the home owner to reset the DW cycle everytime the GB was used. And you would have the HO curse your name every time they remembered that you cheaped out and didn't run a circuit for the extra $25 dollars of material and minimal effort. (Not that 'they' would know that, but you would...)

Common practice to just run a 3-wire to the sink for the both as a give-in. Priced that way off the bat. That way you're covered if they up-grade the appliances after rough, or anytime in the future.


Mark Heller
"Well - I oughta....." -Jackie Gleason
#94731 08/10/05 09:57 PM
Joined: Apr 2002
Posts: 7,382
Likes: 7
Member
Guys:
Just a heads-up; check the nameplate on the DW. 9.1 amps total load; hmm....15 amp OCP
CHECK the nameplate before installing the CB,

GD's vary, 4.9 FLA, 8.25 FLA, etc.

Most guys around here run #12 to DW, 15 amp CB; #14 for disposal....H/R. Most DW are hard wired; disposals are probably a 50/50 mix.

John


John
#94732 08/14/05 06:21 PM
Joined: Jun 2004
Posts: 24
R
Member
Around here we just put the garbage disposal on one of the 2 required appliance circuits and the dishwasher usually gets its own 15 or 20 Amp circuit.It really works well-absolutely no callbacks!

#94733 08/14/05 07:41 PM
Joined: May 2003
Posts: 2,876
E
e57 Offline
Member
Rhino - No other outlets.... Means no GB/DW, etc. Refers and ignitors for rangetops are an exception and Din rm/ pantry plugs.

Quote
210.52(2) No Other Outlets. The two or more small-appliance branch circuits specified in 210.52(B)(1) shall have no other outlets.


Mark Heller
"Well - I oughta....." -Jackie Gleason