0 members (), 533 guests, and 35 robots.
I agree with John. It is perfectly acceptable to use a panel with that has a buss rating higher than the feeder. One thing to be careful about is the lug rating of 200 amp loadcenters since the minimum wire size for many of them is #1. I believe the lugs on 200 and 225 amp Square D loadcenters are rated down to #6.
Curt
[This message has been edited by caselec (edited 08-06-2005).]
Curt Swartz
BobH, I don't know if you're asking about the 200-amp main, or the 200-amp minimum service. I've done the setup that Steve describes, and consider it an additional disconnect. Personally I LIKE having an additional disconnect within sight in that situation.
The 200-amp minimum isn't an NEC requirement, but a local amendment. One town will allow 100-amp if you provide load calculations. I prefer to go with the 200-amp service than to do calculations. It's more time involved to make less money and I'd look like a fool if the additional service were needed in the future.
Dave
ShockMe77, you have shocked me. [Linked Image]
I think article 110.3 applies here.
I think that is a major stretch.
110.3 Examination, Identification, Installation, and Use of Equipment.
(A) Examination. In judging equipment, considerations such as the following shall be evaluated:
(7) Classification by type, size, voltage, current capacity, and specific use
Notice it says "considerations such as"
Most reasonable people IMO would consider a 200 amp panel to be safe fed with a 90 amp breaker.
Would you require a 200 amp disconnect feeding a 125 amp load to be fed at 200 amps?
Bob
A similar situation IMO is running a 60-amp AC disconnect at 30-amps.
Dave
X
ever thought of just useing a main-lug 200A?
