Receptacles at floor to ceiling windows (dwelling) #93897
06/23/05 12:42 PM
06/23/05 12:42 PM
C
cgw  Offline OP
Member
Joined: Jul 2004
Posts: 134
Rochester NY
Anyone run into a situation where a house has floor to ceiling 16 foot long windows?
The only way to get receptacles 12' on centers is either a floor outlet or something in the window frame at the floor.

2017 / 2014 NEC & Related Books and Study Guides
Re: Receptacles at floor to ceiling windows (dwelling) #93898
06/23/05 04:18 PM
06/23/05 04:18 PM
E
energy7  Offline
Member
Joined: Jun 2002
Posts: 58
Oxnard, CA, USA
cgw,
Yes, I encounter this with custom beachfront homes that want that "wonderful" view. Very typically, they have 16 ft+ wide glass, with two sliding panels in the center, and fixed glass on the sides. Part of the problem is structural: they have a rigid frame of steel columns on each side, steel beam overhead, and slab floor. No convenient place to place a receptacle within 72" of the edge of the opening.
I try to catch this in plan check, so the floor boxes can be cast in the concrete slab. Otherwise, our overworked combo inspectors have to try to catch it in the field.

Re: Receptacles at floor to ceiling windows (dwelling) #93899
06/23/05 08:56 PM
06/23/05 08:56 PM
E
e57  Offline
Member
Joined: May 2003
Posts: 2,876
S.F.,CA USA
Sounds like you'll have add a floor recept...

Quote
210.52(2) Wall Space. As used in this section, a wall space shall include the following:
(1) Any space 600 mm (2 ft) or more in width (including space measured around corners) and unbroken along the floor line by doorways, fireplaces, and similar openings
(2) The space occupied by fixed panels in exterior walls, excluding sliding panels
(3) The space afforded by fixed room dividers such as freestanding bar-type counters or railings


Just remember it need to be within 18" of the window to count.

Funny, I just posted the same quote in a different post, just needed to hit paste again...


Mark Heller
"Well - I oughta....." -Jackie Gleason
Re: Receptacles at floor to ceiling windows (dwelling) #93900
06/23/05 10:35 PM
06/23/05 10:35 PM
renosteinke  Offline
Cat Servant
Member
Joined: Jan 2005
Posts: 5,316
Blue Collar Country
This has the same reply as I would give to the curent thread about a balcony:
Maybe there's a place for wiremold/plugmold after all.

Re: Receptacles at floor to ceiling windows (dwelling) #93901
06/24/05 06:36 AM
06/24/05 06:36 AM
J
JoeRossi  Offline
Member
Joined: Jan 2003
Posts: 26
Washington, NJ
Most of the builders in our township apply for a variance so they don't have to put a floor outlet in. I see nothing unsave about it and they are will to pay $250 to have it omitted.


Joe Rossi
Re: Receptacles at floor to ceiling windows (dwelling) #93902
06/24/05 04:17 PM
06/24/05 04:17 PM
E
energy7  Offline
Member
Joined: Jun 2002
Posts: 58
Oxnard, CA, USA
Joe,
Let none of those builders come to my town and try to buy their way out of code compliance. 210-52 is there in large part to avoid the use of extension cords.
The majority of residential fire investigations I've been a part of in one fashion or other have been electrical in origin. Many, many of those were as a direct use and miss use of extension cords. Yes there is a safety issue, otherwise the requirement would not be codified.
Overheating due to load or crimping under the chair or sofa leg is a common origin of fire involving extension cords.

Re: Receptacles at floor to ceiling windows (dwelling) #93903
06/24/05 04:46 PM
06/24/05 04:46 PM
G
George Little  Offline
Member
Joined: Jan 2004
Posts: 1,493
Michigan USA
Any appeals board worth their salt will only waive code requirements when the applicant can offer an equivalent offering to code compliance. Been there- Done that.


George Little
Re: Receptacles at floor to ceiling windows (dwelling) #93904
06/24/05 10:03 PM
06/24/05 10:03 PM
E
e57  Offline
Member
Joined: May 2003
Posts: 2,876
S.F.,CA USA
$250!

A cheap single outlet floor box is <$20! Even my slowest guy could pipe it for <$100 total. (Not including crazy mark-up for time trying to talk me out of it.)

Now don't get me wrong... I've been through this with big windows before, and... I am the code authority on my jobs, until the inspector shows up, or I call him, not the customer. If the inspector is willing to write it out on the card, I'm fine with it. And the time it takes to debate the definition of the code, with the customer, then the inspector, who only says to put it in... Somebody gets charged for that... It could run ya $250 just to waste my time, then still have to pay for the outlet.


Mark Heller
"Well - I oughta....." -Jackie Gleason
Re: Receptacles at floor to ceiling windows (dwelling) #93905
06/25/05 10:52 AM
06/25/05 10:52 AM
G
George  Offline
Member
Joined: Feb 2002
Posts: 375
As I recall and I am unwilling to look at the code but my reading of the code allows:

The 6' rule may be used to compute the number of recepts required. The recepts can then be placed where needed in the room.

Using my reading or asking for a variance seems to be harmless.

Re: Receptacles at floor to ceiling windows (dwelling) #93906
06/25/05 11:37 PM
06/25/05 11:37 PM
renosteinke  Offline
Cat Servant
Member
Joined: Jan 2005
Posts: 5,316
Blue Collar Country
Let me repeat my earlier suggestion...but first.....the rule is that no point on the wall (where it mets the floor) can be more than six feet (measured along the floor line) from a receptacle.....and the receptacle can be as far as 18" into the floor or 66" up the wall.

What I have done in similar situations is install sections of "plugmold." The sections are connected with "wiremold" of the same dimensions as the "plugmold," so there is a nice, clean line. These are mounted on the window frame. If painted appropriately, they appear to be a part of the window.

Somebody should inscribe on every architect's license: "Artists do paintings- not buildings."

Page 1 of 2 1 2

Featured:

2017 Master Electrician Exam Preparation Combos
2017 NEC Electrician
Exam Prep Combos:
Master / Journeyman

 

Member Spotlight
HCE727
HCE727
Delaware County, PA, USA
Posts: 186
Joined: November 2005
Show All Member Profiles 
Top Posters(30 Days)
Popular Topics(Views)
254,521 Are you busy
190,760 Re: Forum
180,480 Need opinion
Powered by UBB.threads™ PHP Forum Software 7.6.1
(Release build 20180101)
Page Time: 0.023s Queries: 15 (0.004s) Memory: 1.0269 MB (Peak: 1.2038 MB) Zlib enabled. Server Time: 2019-04-22 01:10:57 UTC