I believe that the word "approval" is properly used.
The breakers have been tested with "favorable regard".
|
|
|
|
Joined: Aug 2003
Posts: 1,374
Moderator
|
See the article 100 definition.
Ryan Jackson, Salt Lake City
|
|
|
|
Joined: Feb 2005
Posts: 693
Member
|
I see a couple of issues in the larger images:
White wire on top-right breaker w/o being re-colored.
It looks like that breaker is a Thomas & Betts.
What about the re-used breaker on the left?
Back-fed breaker as nain w/o hold-down hardware.
Two aluminum conductors in one top-right terminal. (Anti-ox?)
Larry Fine Fine Electric Co. fineelectricco.com
|
|
|
|
Joined: Jul 2005
Posts: 56
Member
|
Actually they look like forgeries. If so the labeling is also forged and probably have never been tested for anything.
|
|
|
|
Joined: Aug 2005
Posts: 49
Member
|
Is that the transformer for the doorbell that is hooked directly onto the box?
|
|
|
|
Joined: Aug 2003
Posts: 1,374
Moderator
|
Is that the transformer for the doorbell that is hooked directly onto the box? Yes, but that is not a violation.
Ryan Jackson, Salt Lake City
|
|
|
|
Joined: Aug 2005
Posts: 49
Member
|
Heh. Didn't think it was being that the panel is a j-box but hehe. Man if I did that I would never hear the end of it.
|
|
|
|
Joined: Dec 2003
Posts: 886
Member
|
Hmmm, looks like the black from the doorbell transformer is together with the branch circuit on that last breaker. Two wires on the same lug.
-Hal
|
|
|
|
Joined: Sep 2004
Posts: 167
Member
|
Hey Ryan Look real close. You can barely see it. Reference the other c/b's in the larger photo. Maybe the lighting makes it hard to see.
They looked good to me at first until I looked up 240.81
Larry LeVoir Inspector City of Irvine, CA
|
|
|
|
Joined: Feb 2005
Posts: 693
Member
|
Sandy, if you look carefully, it appears someone (Joe?) has covered the words "on" and "off" with little rectangles of electrical tape.
I know for a fact that the Siemens and Murray breakers that use these cases have the words molded into the plastic; look next to the CSA.
Right, Joe?
Larry Fine Fine Electric Co. fineelectricco.com
|
|
|