0 members (), 779 guests, and 13 robots.
So your saying that if a house is being built and they use wood paneling ,they would have to sheetrock it first?
What about those log homes , romex is channeled through them.
Workgear for Electricians
334.10(3) pertains to "other structures"
Not dwellings.
shortcircuit
Type NMC cable is specifically permitted in agricultural buildings.
547.5 Wiring Methods.
(A) Wiring Systems. Types UF, NMC, copper SE cables, jacketed Type MC cable, rigid nonmetallic conduit, liquidtight flexible nonmetallic conduit, or other cables or raceways suitable for the location, with approved termination fittings, shall be the wiring methods employed. Article 398 and Article 502 wiring methods shall be permitted for areas described in 547.1(A).
Tom Horne
[This message has been edited by tdhorne (edited 06-09-2005).]
Tom Horne
Tom- You'll not find NMC being manufactured to my knowledge by onyone. Next best thing if you are not faced with a subject to physical damage would be UF cable.
George Little
Messed up on that one.
George, that was my impression the last time I went on a search for NMC. The wire manufacturers shunt you off to a UF product. They are pretty much saying NMC is UF from the manufactuer's standpoint.
Is there anything NMC can do that UF can't?