Horse Barn Wiring Methods #93735
06/08/05 07:15 PM
06/08/05 07:15 PM
S
shortcircuit  Offline OP
Member
Joined: Jun 2004
Posts: 610
massachusetts
Is romex (NM) allowed to be used in the walls and ceilings of a horse barn in areas specified by 547.1 where it will be concealed by a finish surface such as wood on the walls and plastered ceilings?

shortcircuit

2017 / 2014 NEC & Related Books and Study Guides
Re: Horse Barn Wiring Methods #93736
06/08/05 07:41 PM
06/08/05 07:41 PM
G
Gregtaylor  Offline
Member
Joined: Mar 2005
Posts: 212
Boise, Idaho, USA
The way I read it, I think you're OK.

Re: Horse Barn Wiring Methods #93737
06/09/05 02:02 PM
06/09/05 02:02 PM
S
shortcircuit  Offline OP
Member
Joined: Jun 2004
Posts: 610
massachusetts
Can anyone explain what the last sentance of 334.10(3) means or maybe have a link to such list as described?

"Cables shall be concealed within walls, floors, or ceilings that provide a thermal barrier of material that has at least a 15-minute finish rating as identified in listings of fire-rated assemblies."

My concern is if romex (NM) is concealed behind finish walls of wood on the interior of a horse barn, is the wood wall finish acceptable as a 15-minute fire-rated assembly?

shortcircuit

Re: Horse Barn Wiring Methods #93738
06/09/05 03:04 PM
06/09/05 03:04 PM
E
earlydean  Offline
Member
Joined: Dec 2003
Posts: 751
Griswold, CT, USA
As I recall, 1/2 inch wallboard has a 15 minute rating.
Let me check the UL book for others.


Earl
Re: Horse Barn Wiring Methods #93739
06/09/05 03:17 PM
06/09/05 03:17 PM
E
earlydean  Offline
Member
Joined: Dec 2003
Posts: 751
Griswold, CT, USA
Nope, no wood. All the listed assemblies are gypsum wallboard, plaster, cement block, masonry or 24 gauge metal panels.


Earl
Re: Horse Barn Wiring Methods #93740
06/09/05 03:19 PM
06/09/05 03:19 PM
E
earlydean  Offline
Member
Joined: Dec 2003
Posts: 751
Griswold, CT, USA
Oh yeah, and concrete.


Earl
Re: Horse Barn Wiring Methods #93741
06/09/05 03:53 PM
06/09/05 03:53 PM
E
earlydean  Offline
Member
Joined: Dec 2003
Posts: 751
Griswold, CT, USA
Now you got me going.

My rule of thumb is just not sufficient. the finish ratings go all over the chart, depending on the manufacturer and the product. Examples: American Gypsum Co. 5/8 inch Gypsum board Types AGX-1,2&3 have 23 minute finish ratings. AGX-5 has a 26 minute finish rating. US Gypsum Co. 1/2 inch Gypsum Wallboard (GWB) Types AR, FRX-G, SCX, SHX or WRX all have a 29 minute finish rating.
There are hundreds more. But, the lowest rating I could find for 1/2 inch GWB was 20 minutes. The rating for some 3/8 inch GWB was 8 minutes, so watch out!
The assembly also required paper tape over the joints, and usually a minimum of 2 coats of joint finishing compound.

Sounds like, to make your installation code compliant, you need to add 1/2 GWB over the walls of the barn where you have run the romex.


Earl
Re: Horse Barn Wiring Methods #93742
06/09/05 04:12 PM
06/09/05 04:12 PM
E
earlydean  Offline
Member
Joined: Dec 2003
Posts: 751
Griswold, CT, USA
You can research them yourself at: http://www.ul.com/fire/building.html
Click on the picture of the front cover of the building materials directory.


Earl
Re: Horse Barn Wiring Methods #93743
06/09/05 04:15 PM
06/09/05 04:15 PM
E
earlydean  Offline
Member
Joined: Dec 2003
Posts: 751
Griswold, CT, USA
http://database.ul.com/cgi-bin/XYV/...d=1074327030&cfgid=1073741824&ve rsion=versionless&parent_id=1073984818&sequence=1


Earl
Re: Horse Barn Wiring Methods #93744
06/09/05 04:58 PM
06/09/05 04:58 PM
S
shortcircuit  Offline OP
Member
Joined: Jun 2004
Posts: 610
massachusetts
Thanx earlydean, but I couldn't navigate through to where I could find specific listings on sheetrock and wood?

shortcircuit

Page 1 of 2 1 2

Featured:

2017 Master Electrician Exam Preparation Combos
2017 NEC Electrician
Exam Prep Combos:
Master / Journeyman

 

Member Spotlight
Attic Rat
Attic Rat
Bergen Co.,N.J. USA
Posts: 524
Joined: December 2003
Show All Member Profiles 
Top Posters(30 Days)
Admin 5
Popular Topics(Views)
257,104 Are you busy
192,935 Re: Forum
182,593 Need opinion
Powered by UBB.threads™ PHP Forum Software 7.6.1
(Release build 20180101)
Page Time: 0.024s Queries: 15 (0.004s) Memory: 1.0229 MB (Peak: 1.1976 MB) Zlib enabled. Server Time: 2019-07-19 08:08:15 UTC