#93595 06/02/05 11:00 PM
I think you need some means of disconnecting the circuits at the detached building if there is more than one circuit
#93596 06/02/05 11:19 PM
Got a disconnect in the detached garage DPST switch.
George Little
#93597 06/06/05 06:08 PM
Iwire, how did you run one side of a multiwire circuit feeding a 30a load, and the other feeding a 20a load?
Do they make such a combination 30/20 2pole breaker?
Dnk....
#93598 06/06/05 06:22 PM
Doesn't have to be a two pole breaker.
George Little
#93599 06/06/05 08:04 PM
George you are right.
It can be a fused disconnect, but why?
They also can be single pole breakers with approved handle ties, but that would make it a 2 pole breaker for all pratical purposes.
So I ask again, Do they make 30/20 combinations 2 pole breakers?
Dnk.........
#93600 06/06/05 08:10 PM
I have never seen one, there would be to little call for it.
I did not need or use handle ties, I don't remember if the 20 and 30 amp breakers where even side by side.
#93601 06/06/05 08:15 PM
Dnk, there is no reason for both OCPD's to open both ungrounded conductors at the same time in this circuit.
Roger
#93602 06/06/05 08:19 PM
Is that because they are not on the same yoke?
#93603 06/06/05 08:39 PM
Dnk, yes. Reference 210.4(B)and 210.7(C) in the latter a multiwire branch circuit may not fit the discription. [Linked Image] (further discussion? [Linked Image])