Disconnect for each building #93376
05/19/05 10:22 PM
05/19/05 10:22 PM
M
mhulbert  Offline OP
Member
Joined: Oct 2004
Posts: 132
Anaheim, CA USA
I am ruuning power to a shower building at a camp. Exactly 8' away is another building (restrooms) that need power as well. I am mounting a 3R subpanel on the exterior of the shower building, on the wall facing the restrooms. Is it sufficient to use this subpanel as the disconnecting means for the restroom building, or should they get their own subpanel as well? There will be 3 circuits going into the restrooms. I know that I have to ground the piping + a ground rod at both of the buildings, however, it makes little sense to put up 2 subpanels 8' apart, when one will have more than enough capacity to serve both buildings.

Is 230.70 the right section to be reading for feeds to outbuildings? It says services, but I seem to remember part of the code referring me back to 230.70 when dealing with disconects on seperate structures.
Any help is apreciated!
Mike

2017 / 2014 NEC & Related Books and Study Guides
Re: Disconnect for each building #93377
05/20/05 05:05 AM
05/20/05 05:05 AM
S
shortcircuit  Offline
Member
Joined: Jun 2004
Posts: 610
massachusetts
According to 225.30, you will need a seperate feeder with a disconnect (225.31) at each building or structure, and it must be suitable for use as service equipment (225.36)

shortcircuit

Re: Disconnect for each building #93378
05/20/05 10:09 AM
05/20/05 10:09 AM
renosteinke  Offline
Cat Servant
Member
Joined: Jan 2005
Posts: 5,316
Blue Collar Country
"sub panel" and "disconnect" can be one and the same. Not only do some models allow you to replace the switch with breakers, the advent of hot tubs has led to the offering of many small (2 or 4 space) panels- all suitable for outside use.

Re: Disconnect for each building #93379
06/02/05 10:32 PM
06/02/05 10:32 PM
T
tdhorne  Offline
Member
Joined: Mar 2001
Posts: 345
Maryland, USA
That second building can only have one source of supply. None of the exceptions apply to your situation. The code does not permit you to run multiple general use branch circuits from one building to another.
--
Tom Horne

225.30 Number of Supplies.
Where more than one building or other structure is on the same property and under single management, each additional building or other structure served that is on the load side of the service disconnecting means shall be supplied by one feeder or branch circuit unless permitted in 225.30(A) through (E). For the purpose of this section, a multiwire branch circuit shall be considered a single circuit.

Dam, Tom, Learn to read Shortcircuit already said that.

[This message has been edited by tdhorne (edited 06-02-2005).]


Tom Horne

"This alternating current stuff is just a fad. It is much too dangerous for general use" Thomas Alva Edison

Featured:

2017 Master Electrician Exam Preparation Combos
2017 NEC Electrician
Exam Prep Combos:
Master / Journeyman

 

Member Spotlight
sbi
sbi
indiana
Posts: 47
Joined: March 2008
Show All Member Profiles 
Top Posters(30 Days)
Admin 2
Khombo 2
Popular Topics(Views)
255,884 Are you busy
191,858 Re: Forum
181,623 Need opinion
Powered by UBB.threads™ PHP Forum Software 7.6.1
(Release build 20180101)
Page Time: 0.022s Queries: 14 (0.004s) Memory: 0.9611 MB (Peak: 1.0921 MB) Zlib enabled. Server Time: 2019-06-27 10:32:06 UTC