#93376 05/19/05 10:22 PM
Joined: Oct 2004
Posts: 132
M
Member
I am ruuning power to a shower building at a camp. Exactly 8' away is another building (restrooms) that need power as well. I am mounting a 3R subpanel on the exterior of the shower building, on the wall facing the restrooms. Is it sufficient to use this subpanel as the disconnecting means for the restroom building, or should they get their own subpanel as well? There will be 3 circuits going into the restrooms. I know that I have to ground the piping + a ground rod at both of the buildings, however, it makes little sense to put up 2 subpanels 8' apart, when one will have more than enough capacity to serve both buildings.

Is 230.70 the right section to be reading for feeds to outbuildings? It says services, but I seem to remember part of the code referring me back to 230.70 when dealing with disconects on seperate structures.
Any help is apreciated!
Mike

Stay up to Code with the Latest NEC:


2020 NEC & Related Reference & Study Guides
2020 NEC & Related Reference & Study Guides
Pass Your Exam the FIRST TIME with these Exam Prep Combos:
 

>> Master Electrician Exam Prep     >> JourneyMan Electrician Exam Prep
 

Joined: Jun 2004
Posts: 613
S
Member
According to 225.30, you will need a seperate feeder with a disconnect (225.31) at each building or structure, and it must be suitable for use as service equipment (225.36)

shortcircuit

Joined: Jan 2005
Posts: 5,390
Likes: 1
Cat Servant
Member
"sub panel" and "disconnect" can be one and the same. Not only do some models allow you to replace the switch with breakers, the advent of hot tubs has led to the offering of many small (2 or 4 space) panels- all suitable for outside use.

Joined: Mar 2001
Posts: 345
T
Member
That second building can only have one source of supply. None of the exceptions apply to your situation. The code does not permit you to run multiple general use branch circuits from one building to another.
--
Tom Horne

225.30 Number of Supplies.
Where more than one building or other structure is on the same property and under single management, each additional building or other structure served that is on the load side of the service disconnecting means shall be supplied by one feeder or branch circuit unless permitted in 225.30(A) through (E). For the purpose of this section, a multiwire branch circuit shall be considered a single circuit.

Dam, Tom, Learn to read Shortcircuit already said that.

[This message has been edited by tdhorne (edited 06-02-2005).]


Tom Horne

"This alternating current stuff is just a fad. It is much too dangerous for general use" Thomas Alva Edison

Link Copied to Clipboard
Featured:

Tools for Electricians
Tools for Electricians
 

* * * * * * *
2023 National Electrical Code (NEC)
2023 NEC Now Available!
 
* * * * * * *

2020 Master Electrician Exam Preparation Combos
2020 NEC Electrician
Exam Prep Combos:
Master / Journeyman

 

Member Spotlight
cookcc
cookcc
California ,Long Beach
Posts: 28
Joined: May 2007
Top Posters(30 Days)
BigB 6
Popular Topics(Views)
307,238 Are you busy
235,208 Re: Forum
219,301 Need opinion
Powered by UBB.threads™ PHP Forum Software 7.7.5