#93249 05/10/05 11:15 PM
Joined: Feb 2002
Posts: 2,233
H
Member
I was always told that they were used in order to prevent a "Choke" by bonding the GEC to the metal pipe.

Work Gear for Electricians and the Trades

Workgear for Electricians

#93250 05/11/05 01:28 PM
Joined: Nov 2000
Posts: 2,148
R
Member
Joe,
Quote
See the 1999 NEC Section 250-64(C)
Exception: Busbars shall be permitted to have splices.
Does that exception permit the use of a busbar to splice other grounding electrode conductors, or does it just permit a busbar that is used as the grounding electrode conductor to have splices. I think that it only permits busbars used as GECs to have splices. The change in the 2005 code seems to change this and permit the busbar to be used as a splice point for other GECs.
Don


Don(resqcapt19)
#93251 05/20/05 06:22 PM
Joined: Oct 2000
Posts: 2,749
Member
Don

I think they wanted to say that the GEC could be run to the busbar for splicing as it is now, anyway now it is clear.


Joe Tedesco, NEC Consultant