0 members (), 1,544 guests, and 6 robots.
#93178 05/07/05 01:36 PM
LOL [Linked Image]
Workgear for Electricians
#93179 05/07/05 01:43 PM
Ian How can I argue with a simple straight forward answer like that. [Linked Image]
I wish all NEC issues could be made as clear to me as that.
Bob
#93180 05/07/05 02:20 PM
Thanks Bob, but just curious do you think it could be argued that note 2 of table 250.66 would allow a #10 GEC for a 30 amp sub in a detached building?
#93181 05/07/05 04:04 PM
No I do not believe note 2 will provide any relief in this instance.
#93182 05/07/05 04:59 PM
I believe that, for a sub-panel, you're stuck with #8 to the ground rod. Remember, the ground rod is there for lightning, and has little to do with the service size.
The introduction to the code make it clear that the code is not a design manual, nor is it intended to allow for future growth, etc. With that in mind, I submit that, as a professional who is paid for his judgement as much as anything else, you should make these allowances, and exceed code minimums.
That is, run a big pipe -1" at least- and mount at least an A/C disconnect....at some future date, either the wire will go bad, or the customer will want more. How many garages are really workshops, after all? The $$$ for this improvement over code are minimal, and reap huge dividends down the line.
Or do you like digging? :-)
#93183 05/07/05 05:41 PM
Bob, the operative question is "did you bond the fence?" If it is bonded at both ends you have a metalic path. Otherwise it is not an issue.
You can even make it more interesting. If the fence is now a wall with a footer (>20' of steel) do you have to stub up a grounding electrode conductor while the steel is "available"?
#93184 05/07/05 05:55 PM
Greg
Yeah that is kind of a separate issue to what I was half joking about.
A simple breezeway connection between these buildings would change the rules.
Why wouldn't a wood fence do the same thing if connected to each building?
It is just an odd rule.
But as you said the rules are the rules. [Linked Image]
Bob
#93185 05/08/05 01:03 AM
I guess I actually try to see the hazard addressed when I look at rules. I can see "bonded" metalic paths being an issue because you are paralleling the neutral down that metalic path. If this is an unbonded piece of metal it is not really a path. The only path back is down the grounded wire in the 3 wire feeder.
#93186 05/08/05 08:43 AM
Y
George
225.36 Exception :for Garages and outbuildings on RESIDENTIAL proprety a Snap switch or SET of 3way or 4 way snap switches Shall be PERMITTED as the disconnecting means.
So by that sentence why would Residential not apply????
So Why couldn't two Snap switchs be used as disconnects???Or even a 2 pole switch???
If this is a Mulit wire branch cicuit I feel there'd be no problem.
[This message has been edited by Yoopersup (edited 05-08-2005).]