Bob Badger Construction & Maintenance Electrician Massachusetts
|
|
|
|
Joined: Jan 2003
Posts: 4,391
Moderator
|
Ian How can I argue with a simple straight forward answer like that. I wish all NEC issues could be made as clear to me as that. Bob
Bob Badger Construction & Maintenance Electrician Massachusetts
|
|
|
|
Joined: Feb 2004
Posts: 133
Member
|
Thanks Bob, but just curious do you think it could be argued that note 2 of table 250.66 would allow a #10 GEC for a 30 amp sub in a detached building?
|
|
|
|
Joined: Jan 2003
Posts: 4,391
Moderator
|
No I do not believe note 2 will provide any relief in this instance.
Bob Badger Construction & Maintenance Electrician Massachusetts
|
|
|
|
Joined: Jan 2005
Posts: 5,445 Likes: 3
Cat Servant Member
|
I believe that, for a sub-panel, you're stuck with #8 to the ground rod. Remember, the ground rod is there for lightning, and has little to do with the service size.
The introduction to the code make it clear that the code is not a design manual, nor is it intended to allow for future growth, etc. With that in mind, I submit that, as a professional who is paid for his judgement as much as anything else, you should make these allowances, and exceed code minimums.
That is, run a big pipe -1" at least- and mount at least an A/C disconnect....at some future date, either the wire will go bad, or the customer will want more. How many garages are really workshops, after all? The $$$ for this improvement over code are minimal, and reap huge dividends down the line. Or do you like digging? :-)
|
|
|
|
Joined: Jul 2004
Posts: 9,931 Likes: 34
Member
|
Bob, the operative question is "did you bond the fence?" If it is bonded at both ends you have a metalic path. Otherwise it is not an issue. You can even make it more interesting. If the fence is now a wall with a footer (>20' of steel) do you have to stub up a grounding electrode conductor while the steel is "available"?
Greg Fretwell
|
|
|
|
Joined: Jan 2003
Posts: 4,391
Moderator
|
Greg Bob, the operative question is "did you bond the fence?" If it is bonded at both ends you have a metalic path. Yeah that is kind of a separate issue to what I was half joking about. A simple breezeway connection between these buildings would change the rules. Why wouldn't a wood fence do the same thing if connected to each building? It is just an odd rule. But as you said the rules are the rules. Bob
Bob Badger Construction & Maintenance Electrician Massachusetts
|
|
|
|
Joined: Jul 2004
Posts: 9,931 Likes: 34
Member
|
I guess I actually try to see the hazard addressed when I look at rules. I can see "bonded" metalic paths being an issue because you are paralleling the neutral down that metalic path. If this is an unbonded piece of metal it is not really a path. The only path back is down the grounded wire in the 3 wire feeder.
Greg Fretwell
|
|
|
|
Joined: Mar 2003
Posts: 849
Member
|
George 225.36 Exception :for Garages and outbuildings on RESIDENTIAL proprety a Snap switch or SET of 3way or 4 way snap switches Shall be PERMITTED as the disconnecting means. So by that sentence why would Residential not apply???? So Why couldn't two Snap switchs be used as disconnects???Or even a 2 pole switch??? If this is a Mulit wire branch cicuit I feel there'd be no problem.