Grounding #93060 04/28/05 01:08 PM
Joined: Apr 2005
Posts: 73
D
dlhoule Offline OP
Member
My facility recently replaced a hot water heater. This is a 3 phase 440 Volt heater.
The original water supply to this heater was galvenized pipe. It has been replaced with plastic. I am of the opinion that it would be a lot safer to pull in a ground wire, rather than rely on conduit for grounding. This conduit has been there for over 30 years and we have had several roof leaks with conduit getting wet and corroded. What would be your recommendations for this?

2017 / 2014 NEC & Related Books and Study Guides
Re: Grounding #93061 04/29/05 10:39 AM
Joined: Apr 2002
Posts: 7,218
HotLine1 Offline
Member
Welcome to ECN.
Our 'standard' practice is to "pull a ground".

Also, don't forget to 'jump' the metalic hot and cold water lines, as you may have 'lost' the grd bond with the replacement htr.

John


John
Re: Grounding #93062 04/30/05 04:43 AM
Joined: Jan 2003
Posts: 4,391
I
iwire Offline
Moderator
Quote
don't forget to 'jump' the metallic hot and cold water lines

While this is never a bad thing to do there is no specific requirement in the NEC to do so. [Linked Image]

The metal water piping systems are required to be bonded however there is no reason that must happen at the water heater or that a bonding conductor must be installed.

The hot and cold water pipes are very likely to already be bonded together at tub and shower valves, laundry valves, mixing valves at the boiler etc.

If we say those are not reliable connections we might as well put a bonding jumper around every soldered connection.

For what it's worth here is the 2002 Handbook commentary.

Quote
If it cannot reasonably be concluded that the hot and cold water pipes are reliably interconnected, an electrical bonding jumper is required to ensure that this connection is made. Some judgment must be exercised for each installation. The special installation requirements provided in 250.64(A), (B), and (E) also apply to the water piping bonding jumper.

Hey John I am not picking on you here, this is just a pet peeve of mine when I see inspectors say the hot and cold must be bonded at the water heater.


Bob


Bob Badger
Construction & Maintenance Electrician
Massachusetts
Re: Grounding #93063 04/30/05 05:37 AM
Joined: Apr 2005
Posts: 73
D
dlhoule Offline OP
Member
Thanks John & Iwire, just a point of info. This heater is for shower facilities. Original was installed in the sixties at which time there were no requirements for the hot & cold water lines to be bonded together. In this case I think it is an excellent idea. We now have plastic supplying the heater and galvenized running to the shower and lavatory facilities. John, when you say pulling a ground is standard practice in your area, are you referring to replacement of existing equipment, new equipment or both?

Re: Grounding #93064 05/01/05 07:35 AM
Joined: Feb 2002
Posts: 2,233
H
harold endean Offline
Member
Bob,

I agree with you that the hot and cold water must be bonded together but not at the water heater. If I was inspecting a job and I don't see the jumper wire at the water heater, I would try to look at a boiler or washing machine to see if there is a connection between the two. However for the $5-$7 dollers worth of parts for the bonding wire and clamps, most guys just throw it on. Also if the bonding jumper isn't at the water heater and it is bonded elsewhere, sometimes it is hard to find out where it is bonded. Some AHJ's might not take the extra time to try and find out where it is bonded.


Featured:

2020 National Electrical Code
2020 National Electrical
Code (NEC)

* * * * * * *

2020 Master Electrician Exam Preparation Combos
2020 NEC Electrician
Exam Prep Combos:
Master / Journeyman

 

Member Spotlight
sbi
sbi
indiana
Posts: 47
Joined: March 2008
Show All Member Profiles 
Top Posters(30 Days)
Trumpy 9
Popular Topics(Views)
272,009 Are you busy
205,897 Re: Forum
193,951 Need opinion
Powered by UBB.threads™ PHP Forum Software 7.7.3