ECN Electrical Forum - Discussion Forums for Electricians, Inspectors and Related Professionals

>> Home   >> Electrical-Photos   >> Classifieds   >> Subscribe to Newsletter   >> Store  
 

Photo of the Week:

Mouse on a Bus
Mouse on a Bus

Advertisement:-Left
Recent Gallery Topics:
What in Tarnation?
What in Tarnation?
by timmp, September 10
Plumber meets Electrician
Plumber meets Electrician
by timmp, September 10
Who's Online Now
0 members (), 120 guests, and 25 robots.
Key: Admin, Global Mod, Mod
Previous Thread
Next Thread
Print Thread
Rate Thread
#93060 04/28/05 01:08 PM
Joined: Apr 2005
Posts: 73
D
dlhoule Offline OP
Member
My facility recently replaced a hot water heater. This is a 3 phase 440 Volt heater.
The original water supply to this heater was galvenized pipe. It has been replaced with plastic. I am of the opinion that it would be a lot safer to pull in a ground wire, rather than rely on conduit for grounding. This conduit has been there for over 30 years and we have had several roof leaks with conduit getting wet and corroded. What would be your recommendations for this?

Horizontal Ad
#93061 04/29/05 10:39 AM
Joined: Apr 2002
Posts: 7,412
Likes: 7
Member
Welcome to ECN.
Our 'standard' practice is to "pull a ground".

Also, don't forget to 'jump' the metalic hot and cold water lines, as you may have 'lost' the grd bond with the replacement htr.

John


John
#93062 04/30/05 04:43 AM
Joined: Jan 2003
Posts: 4,391
I
Moderator
Quote
don't forget to 'jump' the metallic hot and cold water lines

While this is never a bad thing to do there is no specific requirement in the NEC to do so. [Linked Image]

The metal water piping systems are required to be bonded however there is no reason that must happen at the water heater or that a bonding conductor must be installed.

The hot and cold water pipes are very likely to already be bonded together at tub and shower valves, laundry valves, mixing valves at the boiler etc.

If we say those are not reliable connections we might as well put a bonding jumper around every soldered connection.

For what it's worth here is the 2002 Handbook commentary.

Quote
If it cannot reasonably be concluded that the hot and cold water pipes are reliably interconnected, an electrical bonding jumper is required to ensure that this connection is made. Some judgment must be exercised for each installation. The special installation requirements provided in 250.64(A), (B), and (E) also apply to the water piping bonding jumper.

Hey John I am not picking on you here, this is just a pet peeve of mine when I see inspectors say the hot and cold must be bonded at the water heater.


Bob


Bob Badger
Construction & Maintenance Electrician
Massachusetts
#93063 04/30/05 05:37 AM
Joined: Apr 2005
Posts: 73
D
dlhoule Offline OP
Member
Thanks John & Iwire, just a point of info. This heater is for shower facilities. Original was installed in the sixties at which time there were no requirements for the hot & cold water lines to be bonded together. In this case I think it is an excellent idea. We now have plastic supplying the heater and galvenized running to the shower and lavatory facilities. John, when you say pulling a ground is standard practice in your area, are you referring to replacement of existing equipment, new equipment or both?

#93064 05/01/05 07:35 AM
Joined: Feb 2002
Posts: 2,233
H
Member
Bob,

I agree with you that the hot and cold water must be bonded together but not at the water heater. If I was inspecting a job and I don't see the jumper wire at the water heater, I would try to look at a boiler or washing machine to see if there is a connection between the two. However for the $5-$7 dollers worth of parts for the bonding wire and clamps, most guys just throw it on. Also if the bonding jumper isn't at the water heater and it is bonded elsewhere, sometimes it is hard to find out where it is bonded. Some AHJ's might not take the extra time to try and find out where it is bonded.


Link Copied to Clipboard
Advertisement:-Right


Tools for Electricians
Tools for Electricians
 

* * * * * * *
2023 National Electrical Code (NEC)
2023 NEC + Exam Prep Study Guides Now Available!
 

Member Spotlight
CDS
CDS
Nicholson Ga
Posts: 34
Joined: June 2006
Top Posters(30 Days)
Popular Topics(Views)
340,263 Are you busy
265,660 Re: Forum
246,668 Need opinion
New Page 2
Powered by UBB.threads™ PHP Forum Software 7.7.5