I just found this site the other day and think it’s great to have a place to air some questions and get some insights on code topics.

I have a question regarding the #8 solid bonding conductor for a pool. I have a customer that has an existing pool and the other day moved the pool pump and heater about 30’ away to the back of a pool cabana. He asked me to relocate the electrical to the back of the cabana as well. I’ll be installing a hand hole to make splices and extend the PVC conduits, however my question is how to extend the #8 solid bond wire since it terminated at the pump. As far as I can see the Code says nothing about the bond wire needing to be “unbroken”. The hand book even shows the pump, railings, diving board, etc being tapped from the run around the pool. The only requirement that I can see in the code is to use a listed pressure connector or clamp or exothermic weld. Since I don’t have the exothermic weld tool available can I use a split bolt rated for direct burial and splice a piece of #8. Or how about a UF splice kit – it’s a pressure connector listed for direct burial (or am I misapplying the term pressure connector?) Any thoughts?

Mic.

Horizontal Ad
Joined: Jul 2004
Posts: 9,992
Likes: 35
G
Member
They use direct burial listed split bolts around here.


Greg Fretwell
Joined: Jan 2004
Posts: 1,507
G
Member
Split bolts here in Michigan too.


George Little
Joined: Apr 2005
Posts: 1
A
Junior Member
The bonding conductor is regularly, and legally connected to the pool reinforcing steel with approved clamps causing a 'breaking' or discontinuation of the conductor. Bonding is a means to assure the equipotential of the conductive surfaces in the pool area, and is different from carrying fault current in service equipment. I would use any kind of equal clamping mechanism, such as a split bolt.


Link Copied to Clipboard
Advertisement:-Right


Tools for Electricians
Tools for Electricians
 

* * * * * * *
2023 National Electrical Code (NEC)
2023 NEC + Exam Prep Study Guides Now Available!
 

Member Spotlight
CharlieE
CharlieE
Indianapolis
Posts: 201
Joined: April 2004
Top Posters(30 Days)
BigB 6
timmp 2
Popular Topics(Views)
329,530 Are you busy
254,376 Re: Forum
236,838 Need opinion
New Page 2
Powered by UBB.threads™ PHP Forum Software 7.7.5