Joined: Apr 2005
Posts: 20
M
Micmann Offline OP
Member
I just found this site the other day and think it’s great to have a place to air some questions and get some insights on code topics.

I have a question regarding the #8 solid bonding conductor for a pool. I have a customer that has an existing pool and the other day moved the pool pump and heater about 30’ away to the back of a pool cabana. He asked me to relocate the electrical to the back of the cabana as well. I’ll be installing a hand hole to make splices and extend the PVC conduits, however my question is how to extend the #8 solid bond wire since it terminated at the pump. As far as I can see the Code says nothing about the bond wire needing to be “unbroken”. The hand book even shows the pump, railings, diving board, etc being tapped from the run around the pool. The only requirement that I can see in the code is to use a listed pressure connector or clamp or exothermic weld. Since I don’t have the exothermic weld tool available can I use a split bolt rated for direct burial and splice a piece of #8. Or how about a UF splice kit – it’s a pressure connector listed for direct burial (or am I misapplying the term pressure connector?) Any thoughts?

Mic.

Stay up to Code with the Latest NEC:


2020 NEC & Related Reference & Study Guides
2020 NEC & Related Reference & Study Guides
Pass Your Exam the FIRST TIME with these Exam Prep Combos:
 

>> Master Electrician Exam Prep     >> JourneyMan Electrician Exam Prep
 

Joined: Jul 2004
Posts: 9,745
Likes: 13
G
Member
They use direct burial listed split bolts around here.


Greg Fretwell
Joined: Jan 2004
Posts: 1,507
G
Member
Split bolts here in Michigan too.


George Little
Joined: Apr 2005
Posts: 1
A
Junior Member
The bonding conductor is regularly, and legally connected to the pool reinforcing steel with approved clamps causing a 'breaking' or discontinuation of the conductor. Bonding is a means to assure the equipotential of the conductive surfaces in the pool area, and is different from carrying fault current in service equipment. I would use any kind of equal clamping mechanism, such as a split bolt.


Link Copied to Clipboard
Featured:

Tools for Electricians
Tools for Electricians
 

* * * * * * *

2020 Master Electrician Exam Preparation Combos
2020 NEC Electrician
Exam Prep Combos:
Master / Journeyman

 

Member Spotlight
electure
electure
Fullerton, CA USA
Posts: 4,289
Joined: December 2000
Top Posters(30 Days)
dsk 3
Popular Topics(Views)
297,409 Are you busy
228,264 Re: Forum
213,161 Need opinion
Powered by UBB.threads™ PHP Forum Software 7.7.5