Member
|
can 15a rec. be wired to a 20a circuit using the feed thru screws on the rec.? or would you have to splice conductors so there is no more than one wire on device?
|
|
|
|
Joined: Jan 2004
Posts: 1,507
Member
|
Only the grounded conductor and then only if it is part of a multiwire branch circuit. 300.13(B). If it were my job I'd pigtail both of the circuit conductors because it's a more reliable job. But, code is minimum and that's what all I can ask for as an inspector.
George Little
|
|
|
|
Joined: Aug 2003
Posts: 1,374
Moderator
|
can 15a rec. be wired to a 20a circuit using the feed thru screws on the rec.? Yes
Ryan Jackson, Salt Lake City
|
|
|
|
Joined: Aug 2001
Posts: 335
Member
|
Gee Ryan ... a one word answer. You must not have had your morning coffee
|
|
|
|
Joined: Feb 2005
Posts: 693
Member
|
The answer is definitely yes. The neutral should be pigtailed if it's part of a multi-wire circuit, unless the breaker handles are tied together.
The only difference between 15- and 20-amp receptacles of the same grade is the 20-amp-plug rejection of the 15-amp receptacle.
In other words, the slot shape is the only difference; the internals are the same. Ever notice that 15-amp GFCI receptacles are feed-thru rated for 20 amps?
Larry Fine Fine Electric Co. fineelectricco.com
|
|
|
|
Joined: Dec 2004
Posts: 52
Member
|
#12 wire will not fit in the stab-in slot on a 15 amp receptacle. It is Code legal to install 15 amp receptacles on a 20 amp circuit if there is more than one receptacle on the circuit--if only one receptacle (or one duplex) then it must be 20 amp rating. Use the screws to attach the wire. Do not pigtail #14 wire on a 20 amp circuit. As for multi-wire circuits, always splice the neutral(solid neutral) whether the handles are tied together or not. It is not required to tie the handles--but I believe it should be required. 20 A receptacles have no stab-in slots. Usually the blade holding hardware is stronger. On 20 A circuits, I pigtail hot, neutral, and ground in each box it speeds up the finish electridal.
|
|
|
|
Joined: Feb 2005
Posts: 693
Member
|
210.4 Multiwire Branch Circuits. (C) Line-to-Neutral Loads. Multiwire branch circuits shall supply only line-to-neutral loads. Exception No. 1: A multiwire branch circuit that supplies only one utilization equipment. Exception No. 2: Where all ungrounded conductors of the multiwire branch circuit are opened simultaneously by the branch-circuit overcurrent device.
210.21 Outlet Devices. Outlet devices shall have an ampere rating that is not less than the load to be served and shall comply with 210.21(A) and (B). (B) Receptacles. (1) Single Receptacle on an Individual Branch Circuit. A single receptacle installed on an individual branch circuit shall have an ampere rating not less than that of the branch circuit.
ARTICLE 100 Definitions Receptacle. A receptacle is a contact device installed at the outlet for the connection of an attachment plug. A single receptacle is a single contact device with no other contact device on the same yoke. A multiple receptacle is two or more contact devices on the same yoke.
300.13 Mechanical and Electrical Continuity — Conductors. (B) Device Removal. In multiwire branch circuits, the continuity of a grounded conductor shall not depend on device connections such as lampholders, receptacles, and so forth, where the removal of such devices would interrupt the continuity.
[This message has been edited by Larry Fine (edited 04-29-2005).]
[This message has been edited by Larry Fine (edited 04-29-2005).]
Larry Fine Fine Electric Co. fineelectricco.com
|
|
|
|
Joined: Jan 2003
Posts: 4,391
Moderator
|
Larry
Handle ties or not 300.13(B) requires the pig tailing of the neutral.
The exception you highlighted, 210.4(C)Exception No. 2 has no influence on the 300.13(B) requirement to pigtail the grounded conductor.
Bob
Bob Badger Construction & Maintenance Electrician Massachusetts
|
|
|
|
Joined: Feb 2005
Posts: 693
Member
|
You're absolutely correct. My apologies.
Larry Fine Fine Electric Co. fineelectricco.com
|
|
|
|
Joined: Aug 2003
Posts: 1,374
Moderator
|
Gee Ryan ... a one word answer. You must not have had your morning coffee
Yeah...you got me there!
Ryan Jackson, Salt Lake City
|
|
|
Posts: 27
Joined: December 2004
|
|
|
|
|