code violation ? #91320
01/10/05 02:27 PM
01/10/05 02:27 PM
M
mj  Offline OP
Member
Joined: Jun 2002
Posts: 186
meriidian, ms
use of the regular plastic outlet boxes that are used for interior wiring ? is a code violation to use these boxes in brick or concreate wall ? Some electrician in my area use the plastic boxes in brick and do not sleeve the NMC going through the brick. what code sections is violated her, if any ?

2017 / 2014 NEC & Related Books and Study Guides
Re: code violation ? #91321
01/10/05 05:34 PM
01/10/05 05:34 PM
G
gfretwell  Online Content

Member
Joined: Jul 2004
Posts: 9,368
Estero,Fl,usa
I assume you mean NM-b, most folks have never seen NMC.

I have asked a similar question myself and the closest thing to an answer I found is they consider the wet location to start on the face of the outside wall but I never really had that confirmed.
It is also common to see regular metal device boxes in masonry served by Romex.

It is OK to "fish" Romex through voids in masonry if this is "dry".

I will just sit and watch what you get here.


Greg Fretwell
Re: code violation ? #91322
01/10/05 06:37 PM
01/10/05 06:37 PM
G
George Little  Offline
Member
Joined: Jan 2004
Posts: 1,498
Michigan USA
Okay Greg, here goes. "luminaires installed in a wet or damp locationshall be installed so that water can not accumulate in wiring compartments"
Kinda helps. By definition, the outdoor fixture is in a wet location. I have never seen any other approach to this installation except having the NM cable either enter the box set in the brick or the fixture directly. If I wrote a violation I'm not sure what the installer wouild do to change it. I say don't rock the boat. There is some wording that has us sealing around the box or cover to prevent the entry of water. The reference escapes me.


George Little
Re: code violation ? #91323
01/10/05 06:56 PM
01/10/05 06:56 PM
G
gfretwell  Online Content

Member
Joined: Jul 2004
Posts: 9,368
Estero,Fl,usa
Lee County requires my wife to caulk around the bezel on exterior wall mounted lights.
They still seem to treat the masonry of an exterior wall as dry.


Greg Fretwell
Re: code violation ? #91324
01/10/05 10:32 PM
01/10/05 10:32 PM
H
harold endean  Offline
Member
Joined: Feb 2002
Posts: 2,233
Boonton, NJ
MJ,

I guess the only thing that would prohibit the use of plastic boxes in masonary is the code section 110.3 (B). Is the box listed and labeled for the use? Most likely it is not. Would I red tag the job because of it? Most likely not. As long as there isn't big gaps around the boxes which would allow the water to get inside the masonary wall.

Re: code violation ? #91325
01/11/05 09:31 AM
01/11/05 09:31 AM
R
Reel-Break  Offline
Member
Joined: Apr 2002
Posts: 178
nc
Here we must seal the hole from where the wire leaves the home.And the gasket must be squeezed against the brick to prevent water from entering the wiring compartment.I buy the foam rubber gasket sheets cut them push over the studs then trim after fixture is installed.Haven`t had a issue with plastic vs metal boxes We mostly use metal bnecause they have the clamps and the mason don`t pull the wires out.

Re: code violation ? #91326
01/11/05 05:14 PM
01/11/05 05:14 PM
E
Electricmanscott  Offline
Member
Joined: Jan 2002
Posts: 1,457
Holden, MA USA
I have never sealed an outside fixture other than a flood setup on a weatherproof cover. I suspect if this was such an issue the manufacturers of the fixtures would be required to provide a solution. As for the plastic box I see no big deal. At least it wont rust.

Re: code violation ? #91327
01/11/05 09:38 PM
01/11/05 09:38 PM
S
shortcircuit  Offline
Member
Joined: Jun 2004
Posts: 610
massachusetts
I took a single gang plastic new work nail on box and put screws inside through the back of it into a 2x4 nailed to a concrete wall and ran romex down the 2x4 into the box and this was in a basement on a GFCI circuit.

The inspector made me change the box to a 4inch square steel box. Said the plastic new work box wasn't listed for that type of use.

Is the box your useing listed for your installation?

shortcircuit

Re: code violation ? #91328
01/11/05 09:58 PM
01/11/05 09:58 PM
G
gfretwell  Online Content

Member
Joined: Jul 2004
Posts: 9,368
Estero,Fl,usa
He may have been saying he didn't like the way you attached the box, not the material


Greg Fretwell
Re: code violation ? #91329
01/13/05 06:56 PM
01/13/05 06:56 PM
M
mj  Offline OP
Member
Joined: Jun 2002
Posts: 186
meriidian, ms
This shoud be enforced my using section : 110.3(a)1 suitability . setting a non-metal box in concrete or masonry, per sec #314.23 (G)


Featured:

2017 Master Electrician Exam Preparation Combos
2017 NEC Electrician
Exam Prep Combos:
Master / Journeyman

 

Member Spotlight
noderaser
noderaser
Portland, Oregon, United States
Posts: 404
Joined: March 2007