#91303 01/09/05 11:00 AM
Joined: Dec 2004
Posts: 52
K
kd Offline OP
Member
When I torque lugs using Aluminum wire, I will apply, say 50 ft. lbs., then several days later check the torque. It will be down to, say, 35 lbs, so I re-torque it. Other ECs say you should just torque it and forget it--that the loss in tightness is built-in to the required torque. Of course Copper holds its torque so it is not a problem. What do you guys and gals say about this?

2017 / 2014 NEC & Related Books and Study Guides
#91304 01/09/05 11:47 AM
Joined: Jan 2001
Posts: 1,044
Tom Offline
Member
Torque it once to the specifications for the lug & leave it alone.


Few things are harder to put up with than the annoyance of a good example.
#91305 01/09/05 12:37 PM
Joined: Jan 2004
Posts: 1,507
G
Member
How does an inspector know how much you've torqued a connection? I am a fan of the break away connection.


George Little
#91306 01/10/05 01:38 AM
Joined: Dec 2004
Posts: 86
P
Member
Another reason to not like aluminum as a conductor.


Sam, San Francisco Bay Area
#91307 01/10/05 08:13 PM
Joined: Apr 2001
Posts: 518
J
Member
Not "another" reason- THE reason! Aluminum is notorious for "creep" when over-torqued. Aluminum should not be torqued to the same values as copper for this reason.
Simply put, too much pressure causes the metal to flow, leaving you with a loose connection. Make sure the value you're using is the correct on, and not "something always used."

#91308 01/12/05 01:31 AM
Joined: Dec 2004
Posts: 52
K
kd Offline OP
Member
Aluminum association torque table shows the sasme values for Cooper and Aluminum.

#91309 01/17/05 09:24 PM
Joined: Aug 2001
Posts: 599
N
Member

#91310 01/18/05 12:21 PM
Joined: Nov 2000
Posts: 2,148
R
Member
The following is a very important quote from the document that Nick has posted a link to.
Quote
It is often asked whether bolted connections require periodic retightening. The simple answer is NO. Once the connector is installed with the proper torque, repeated tightening could actually damage the connector and/or the conductor and eventually lead to a failure.
Don


Don(resqcapt19)

Link Copied to Clipboard
Featured:

Tools for Electricians
Tools for Electricians
 

* * * * * * *

2020 Master Electrician Exam Preparation Combos
2020 NEC Electrician
Exam Prep Combos:
Master / Journeyman

 

Member Spotlight
CDS
CDS
Nicholson Ga
Posts: 34
Joined: June 2006
Top Posters(30 Days)
Trumpy 10
Admin 10
Popular Topics(Views)
280,437 Are you busy
213,517 Re: Forum
200,399 Need opinion
Powered by UBB.threads™ PHP Forum Software 7.7.5