I recently cited a double tap (two ungrounded conductors terminating on one 20A breaker) in a service panel as a code violation, but when challanged on it, I can not find it in either the 1999 or the 2002 NEC. I fell like an idiot. Can someone help me out here?


Ray
Stay up to Code with the Latest NEC:


2020 NEC & Related Reference & Study Guides
2020 NEC & Related Reference & Study Guides
Pass Your Exam the FIRST TIME with these Exam Prep Combos:
 

>> Master Electrician Exam Prep     >> JourneyMan Electrician Exam Prep
 

Joined: Jan 2003
Posts: 4,391
I
Moderator
110.3(B) or last sentence of 110.14(A)


Bob Badger
Construction & Maintenance Electrician
Massachusetts
Joined: Mar 2001
Posts: 2,056
R
Member
rkidd,

Before citing "double taps" be sure that the breaker is not designed for 2 terminations.
The double tap was commonly cited when I was doing real eatate work. However, some designs such as the "pressure plate" type of termination (Square D uses this) allow 2 conductors of the same size to be terminated on the breaker.

Joined: Feb 2004
Posts: 133
E
Member
This is one of those things that a lot of people in the trade assume is always a code violation. Not necessarily. It is completly dependent on whether or not the circuit breaker is listed for one or two wire. Many 15 and 20Amp circuit breakers are in fact listed to accomodate 2 wires. Reference the link below from the web site of Mike Holt (who probably has more credability than me [Linked Image]
http://www.mikeholt.com/technical.php?id=nec/unformatted/Jan_ECM&type=u&title=NEC%20-%20Question/Answers%20(1-4-2K)

Joined: Dec 2004
Posts: 2
R
rkidd Offline OP
Junior Member
Thank you all for the speedy replys. With these three answers plus the ref. to the Mike Holt site, I get it. I was barking up the wrong tree thinking I would find something that would say only one branch circuit can be protected by one over current device. Thanks again. Ray


Ray

Link Copied to Clipboard
Featured:

Tools for Electricians
Tools for Electricians
 

* * * * * * *

2020 Master Electrician Exam Preparation Combos
2020 NEC Electrician
Exam Prep Combos:
Master / Journeyman

 

Member Spotlight
Potseal
Potseal
Saskatchewan
Posts: 264
Joined: February 2013
Top Posters(30 Days)
Popular Topics(Views)
297,694 Are you busy
228,493 Re: Forum
213,326 Need opinion
Powered by UBB.threads™ PHP Forum Software 7.7.5