Signs #90758 12/09/04 08:58 PM
Joined: Jan 2004
Posts: 1,507
G
George Little Offline OP
Member
I hope you guys can help me. I putting on a presentation for about 50 inspeectors and I need to know the different places in the codes where we would be required to install signage. This could cover any codes that the electrician may be involved in the installation. Also sign wording would be helpful. Thank you in advance.

[This message has been edited by George Little (edited 12-09-2004).]


George Little
2017 / 2014 NEC & Related Books and Study Guides
Re: Signs #90759 12/09/04 10:38 PM
Joined: Mar 2004
Posts: 98
O
OreElect Offline
Member
600.5 Each commercial building and each commercial occupancy accessable to pedestrians.
When figuring lighting loads,220.3(B)(6)1200 va for each circuit,minimum.
A front and back ped entrance,2 signs.
Within or adj to fountains,see 680.57(C)

Re: Signs #90760 12/09/04 10:43 PM
Joined: Jul 2004
Posts: 9,532
G
gfretwell Offline
Member
Have you got the handbook CD? Do a search on "sign". I got about 50 hits, some I didn't know about.


Greg Fretwell
Re: Signs #90761 12/09/04 10:52 PM
Joined: Feb 2004
Posts: 494
M
mustangelectric Offline
Member
Show windows?

-regards

Greg

Re: Signs #90762 12/10/04 12:12 AM
Joined: Jan 2004
Posts: 1,507
G
George Little Offline OP
Member
I should have been more specific. I was looking for places where you need signage. Like when you have Service equipment in two locations, or when you have two different grounded conductors from different systems in the same raceway etc.


George Little
Re: Signs #90763 12/10/04 03:04 AM
Joined: Jul 2004
Posts: 9,532
G
gfretwell Offline
Member
George, that is what I am talking about. Search on "sign" and you will see a bunch you don't think of.
430.74, 430.113, 490.21, 490.22, 490.44, 513.7, 513.10, 514.11, 518.3, 540.11, 555.13, 620.3 <my mouse finger got tired> ... stuff like that. I didn't see the arc fault sign mentioned so I am sure another search word (like "signs" would find others.
If I had to summarize you need signs for GFCIs, flash hazards, backfed switches, multiple power sources or feeds (utility, generator or "alternate energy" sources), emergency systems, high voltage, various hazmat signs in classified locations, overhead cable warnings (waterways) and cable tray limitations but I am sure I am missing some.

The CD search engine is a good tool to find more. You can put together quite an eye opening show if you tracked them all down and that is just the NEC. Plug in the other NFPA documents, OSHA and state/local rules you might have to have 2 classes. ;-)

[This message has been edited by gfretwell (edited 12-10-2004).]

[This message has been edited by gfretwell (edited 12-10-2004).]


Greg Fretwell
Re: Signs #90764 12/10/04 08:39 AM
Joined: Jan 2004
Posts: 1,507
G
George Little Offline OP
Member
Thanks gfretwell, I guess my second post should have been directed at the comments that directed me to Article 600. I will take your advice and hopefully have enough material for a 2 hour program. I'll take some pictures, quote some code, use PowerPoint and with the inspectors and audience participation, I'm sure I'll be fine. I was hoping someone knew where the information is on labeling the door to Electrical room. Any code that would say that?


George Little
Re: Signs #90765 12/10/04 03:07 PM
Joined: Jul 2004
Posts: 9,532
G
gfretwell Offline
Member
Like 110.34(C) Locked Rooms or Enclosures. The entrances to all buildings, rooms, or enclosures containing exposed live parts or exposed conductors operating at over 600 volts, nominal, shall be kept locked unless such entrances are under the observation of a qualified person at all times.
Where the voltage exceeds 600 volts, nominal, permanent and conspicuous warning signs shall be provided, reading as follows:
DANGER — HIGH VOLTAGE — KEEP OUT


Greg Fretwell
Re: Signs #90766 12/10/04 06:14 PM
Joined: Aug 2003
Posts: 1,374
R
Ryan_J Offline
Moderator
110.16 is always good for discussion/argument.


Ryan Jackson,
Salt Lake City

Featured:

2020 National Electrical Code
2020 National Electrical
Code (NEC)

* * * * * * *

2020 Master Electrician Exam Preparation Combos
2020 NEC Electrician
Exam Prep Combos:
Master / Journeyman

 

Member Spotlight
CDS
CDS
Nicholson Ga
Posts: 34
Joined: June 2006
Show All Member Profiles 
Top Posters(30 Days)
BigB 3
Popular Topics(Views)
270,722 Are you busy
204,962 Re: Forum
193,068 Need opinion
Powered by UBB.threads™ PHP Forum Software 7.7.3