#90632 12/06/04 02:02 PM
Joined: Feb 2004
Posts: 494
M
Member
Hi,
I have 18 - 1" conduits that need to go to a gutter.

314.28(A)(1)covers this right? Only #4 and larger though. Anything smaller and it is based on condcutors right?

I guess a gutter that has no terms in it is a pull box?

Are there specific sections that refer to a "Gutter" or is this the same as "Pull Box"?

Thanks for any replies.

-regrads

MUSTANG


[This message has been edited by mustangelectric (edited 12-06-2004).]

Horizontal Ad
#90633 12/06/04 06:28 PM
Joined: Jan 2001
Posts: 1,044
Tom Offline
Member
See Article 366 and Article 376.

You are allowed a 20% fill and up to 30 current carrying conductors. If you exceed 30 conductors, you have to do the derating per table 310.15(B)(2)(a)

Essentially, they are the same thing, they just differ in how they are used.

Tom

[This message has been edited by Tom (edited 12-06-2004).]

[This message has been edited by Tom (edited 12-06-2004).]


Few things are harder to put up with than the annoyance of a good example.
#90634 12/07/04 04:24 PM
Joined: Feb 2004
Posts: 494
M
Member
Hi,
312.6(A) cover gutters too right?

Thanks for the help.

-regards

Mustang

#90635 12/07/04 06:35 PM
Joined: Aug 2003
Posts: 1,374
R
Moderator
Yes Mustang, 312.6 applies too. There was a change in the 2005 to address this more clearly, stating that the "one wire per terminal" column is to be used, even if you have conductors in parrallel.


Ryan Jackson,
Salt Lake City

Link Copied to Clipboard
Advertisement:-Right


Tools for Electricians
Tools for Electricians
 

Member Spotlight
waymag
waymag
dallas, texas, USA
Posts: 70
Joined: January 2002
Top Posters(30 Days)
Popular Topics(Views)
363,208 Are you busy
286,027 Re: Forum
264,585 Need opinion
New Page 2
Powered by UBB.threads™ PHP Forum Software 7.7.5