NM in conduit #90572 11/30/04 11:58 AM
Joined: Jun 2002
Posts: 58
E
energy7 Offline OP
Member
A comment in the "horse barn" thread has stirred this question.
Can you run NM in conduit for any significant distance. My understanding of 336-6 (and now 334-15) is that conduit protection is used in short runs for specific hazards.
Because NM is a cable assembly and not just conductors, running it in conduit is "mixing wiring methods", and you're subject to overheating.

2017 / 2014 NEC & Related Books and Study Guides
Re: NM in conduit #90573 11/30/04 12:10 PM
Joined: May 2002
Posts: 1,716
R
Roger Offline
Member
This has been cleared up in the 2005 NEC.

It is specifically allowed in the .22 sections of the conduit articles if the particular cable article doesn't prohibit it.

Roger

Re: NM in conduit #90574 11/30/04 12:39 PM
Joined: Jul 2004
Posts: 9,541
G
gfretwell Offline
Member
I don't see how heating is considered an issue at all, code wise. You derate the same in 1/2" conduit as you do in 4" for the same conductor fill. A piece of Romex in "free air" EMT will certainly run cooler than it would buried in insulation in an attic.


Greg Fretwell
Re: NM in conduit #90575 11/30/04 12:50 PM
Joined: Jul 2004
Posts: 9,541
G
gfretwell Offline
Member
the .22 additions only point out rules that always existed. Basically you use the widest dimension of an oval cable as the diameter when computing fill. That is because when you get a twist in it the widest dimension becomes the diameter.


Greg Fretwell
Re: NM in conduit #90576 11/30/04 11:07 PM
Joined: Apr 2001
Posts: 518
J
John Steinke Offline
Member
Romex is listed as a 60 degree assembly.
The THHN wire inside romex is listed as a 90 degree wire.

By putting romex in pipe, you are throwing away 30 degrees of de-rating, before you do anything else.

Also, the inside of conduit can sometimes be considered a wet location; romex is not allowed in wet locations.


Featured:

2020 National Electrical Code
2020 National Electrical
Code (NEC)

* * * * * * *

2020 Master Electrician Exam Preparation Combos
2020 NEC Electrician
Exam Prep Combos:
Master / Journeyman

 

Member Spotlight
Grover
Grover
Sebago, ME, USA
Posts: 109
Joined: January 2005
Show All Member Profiles 
Top Posters(30 Days)
Trumpy 9
Popular Topics(Views)
271,948 Are you busy
205,833 Re: Forum
193,912 Need opinion
Powered by UBB.threads™ PHP Forum Software 7.7.3