#90572 11/30/04 12:58 PM
Joined: Jun 2002
Posts: 58
E
energy7 Offline OP
Member
A comment in the "horse barn" thread has stirred this question.
Can you run NM in conduit for any significant distance. My understanding of 336-6 (and now 334-15) is that conduit protection is used in short runs for specific hazards.
Because NM is a cable assembly and not just conductors, running it in conduit is "mixing wiring methods", and you're subject to overheating.

2017 / 2014 NEC & Related Books and Study Guides
#90573 11/30/04 01:10 PM
Joined: May 2002
Posts: 1,716
R
Member
This has been cleared up in the 2005 NEC.

It is specifically allowed in the .22 sections of the conduit articles if the particular cable article doesn't prohibit it.

Roger

#90574 11/30/04 01:39 PM
Joined: Jul 2004
Posts: 9,653
Likes: 2
G
Member
I don't see how heating is considered an issue at all, code wise. You derate the same in 1/2" conduit as you do in 4" for the same conductor fill. A piece of Romex in "free air" EMT will certainly run cooler than it would buried in insulation in an attic.


Greg Fretwell
#90575 11/30/04 01:50 PM
Joined: Jul 2004
Posts: 9,653
Likes: 2
G
Member
the .22 additions only point out rules that always existed. Basically you use the widest dimension of an oval cable as the diameter when computing fill. That is because when you get a twist in it the widest dimension becomes the diameter.


Greg Fretwell
#90576 12/01/04 12:07 AM
Joined: Apr 2001
Posts: 518
J
Member
Romex is listed as a 60 degree assembly.
The THHN wire inside romex is listed as a 90 degree wire.

By putting romex in pipe, you are throwing away 30 degrees of de-rating, before you do anything else.

Also, the inside of conduit can sometimes be considered a wet location; romex is not allowed in wet locations.


Link Copied to Clipboard
Featured:

Tools for Electricians
Tools for Electricians
 

* * * * * * *

2020 Master Electrician Exam Preparation Combos
2020 NEC Electrician
Exam Prep Combos:
Master / Journeyman

 

Member Spotlight
sparky66wv
sparky66wv
West Virginia
Posts: 2,236
Joined: November 2000
Top Posters(30 Days)
timmp 4
Rachel 4
Popular Topics(Views)
281,407 Are you busy
215,050 Re: Forum
201,934 Need opinion
Powered by UBB.threads™ PHP Forum Software 7.7.5