Thanks fretwell, I didn't get a chance to respond. I was wrapped up with the issue about who could post an entry on this BB. I might add that it is still used in the rural area quite a bit and the incident of vandalism is not a problem. Maybe your average vandal is not comfortable messing with electricity
George Little
|
|
|
|
Joined: Oct 2000
Posts: 2,749
Member
|
Question: Does Type SER have a reduced size neutral like Type SE has? I have not researched the UL directory, but I think that it is 2 sizes smaller, and UL says is can carry the same current. Question: How does UL come up with this? Question: Is anybody here on the UL Council?
Joe Tedesco, NEC Consultant
|
|
|
|
Joined: Jun 2004
Posts: 613
Member
|
Around here SE can be had with a full size neutral and I have never seen SER with a reduced size neutral.
shortcircuit
|
|
|
|
Joined: Jan 2004
Posts: 1,507
Member
|
Same here short circuit- SER comes with three full size insulated conductors and a reduced size bare conductor. SEU is available with a reduced size concentric conductor that is sometimes used as a comon conductor (Neutral) and sometimes used as an equipment grounding conductor.
[This message has been edited by George Little (edited 11-20-2004).]
George Little
|
|
|
|
Joined: Oct 2000
Posts: 2,749
Member
|
I bolded the words I was thinking about. Anyone who wants a PDF file of the UL White Book for 2004 let me know I will send the link. SERVICE CABLE (TXKT) SERVICE ENTRANCE CABLE (TYLZ) This category covers service-entrance cable designated Type SE and Type USE intended for use in accordance with Article 338 of the National Electrical Code, NFPA70. Service-entrance cable, rated 600 V, is Listed in sizes No. 14 AWG and larger for copper, and No. 12 AWG and larger for aluminum or copperclad aluminum. Type SE cable contains Type RHW, RHW-2, XHHW, XHHW-2, THWN or THWN-2 conductors. Type USE cable contains conductors with insulation equivalent to RHW or XHHW. Type USE-2 contains insulation equivalent to RHW-2 or XHHW-2 and is rated 90 C wet or dry. The Type designation of the conductors may be marked on the surface of the cable. When used, this marking indicates that the temperature rating for the cable corresponds to the temperature rating of the conductors. When this marking does not appear, the temperature rating of the cable is 75 C. The cables are designated as follows: Type SE — cable for aboveground installation. Both the individual insulated conductors and the outer jacket or finish of Type SE are suitable for use where exposed to sun. Types USE and USE-2 — cables for underground installation including direct burial in the earth. Cable in sizes No. 4/0 AWG and smaller and having all conductors insulated is suitable for all of the underground uses for which Type UF cable is permitted by the National Electrical Code. Types USE and USE-2 are not suitable for use in premises or aboveground except to terminate at the service equipment or metering equipment. Both the insulation and the outer covering, when used, on single and multiconductor Types USE and USE-2, are suitable for use where exposed to sun. Submersible Water Pump Cable — Indicates a multi-conductor cable in which 2, 3, or 4 single-conductor Type USE or USE-2 cables are provided in a flat or twisted assembly. The cable is Listed in sizes 14 AWG to 4/0 AWG incl., copper, and 12 AWG to 4/0 AWG incl., aluminum or copperclad aluminum. The cable is tag marked ‘‘For use within the well casing for wiring deep well water pumps where the cable is not subject to repetitive handling caused by frequent servicing of the pump units.’’ The insulation may also be surface-marked ‘‘Pump Cable.’’ The cable may be directly buried in the earth in conjunction with this use. Cables that are acceptable for installation in cable trays are so marked. Cables may employ copper, aluminum, or copper-clad aluminum conductors. Cables with copper-clad aluminum conductors are surface printed ‘‘AL (CU-CLAD)’’ or ‘‘Cu-Clad Al.’’ Cables with aluminum conductors are surface printed ‘‘AL.’’ Cables employing compact-stranded copper conductors are so identified directly following the conductor size, wherever it appears (surface, tag, carton, or reel), by ‘‘compact copper.’’ Abbreviations of ‘‘CMPCT’’ and ‘‘CU’’ may be used for compact and copper, respectively. Tags, reels, and cartons for products employing compact-stranded copper conductors have the following marking: ‘‘Terminate with connectors identified for use with compact-stranded copper conductors.’’ For termination information, see Electrical Equipment for Use in Ordinary Locations (AALZ). Based upon tests which have been made involving the maximum heating that can be produced, an uninsulated conductor employed in a service cable assembly is considered to have the same current-carrying capacity as the insulated conductors even though it may be smaller in size. The basic standard used to investigate products in this category is UL 854, ‘‘Service-Entrance Cables.’’ The UL symbol on the product and the Listing Mark of Underwriters Laboratories Inc. on the attached tag, coil, reel or smallest unit container in which the product is packaged is the only method provided by UL to identify these products manufactured under its Listing and Follow-Up Service. The Listing Mark for these products includes the name and/or symbol of Underwriters Laboratories Inc. (as illustrated in the Introduction of this Directory) together with the word ‘‘LISTED,’’ a control number, and one of the following product names as appropriate: A service entrance cable that contains copper or copper-clad aluminum conductor(s) has the product name ‘‘Service-Entrance Cable’’; a service-entrance cable that contains aluminum conductors has the product name ‘‘Aluminum Service-Entrance Cable.’’ edited to remove excess spaces and improve readability [This message has been edited by resqcapt19 (edited 11-21-2004).]
Joe Tedesco, NEC Consultant
|
|
|
|
Joined: Jul 2004
Posts: 9,934 Likes: 34
Member
|
The "uninsulated conductor" in SER is the EGC. The neutral has always been the same size as the ungrounded conductors in the SER I have seen.
Greg Fretwell
|
|
|
|
Joined: Mar 2001
Posts: 345
Member
|
The "uninsulated conductor" in SER is the EGC. The neutral has always been the same size as the ungrounded conductors in the SER I have seen. That may be true when you are using SER for single phase feeders but when you use four conductor SER for three phase services that smaller bare conductor is the neutral. -- Tom H
Tom Horne
"This alternating current stuff is just a fad. It is much too dangerous for general use" Thomas Alva Edison
|
|
|
|
Joined: May 2003
Posts: 2,876
Member
|
This was touched on in a post a while back, and I think we figured out that 250.32 held the answers to this, and allowed two different methods. Not creating parralel paths to ground like egc, gec or metalic water line, would determine if you could do it in the way you described, and where the neutral was bonded. www.markhellerelectric.com/250.32.pdf
Mark Heller "Well - I oughta....." -Jackie Gleason
|
|
|
|
Joined: Jul 2004
Posts: 9,934 Likes: 34
Member
|
Tom I guess Mustang's reference to a residence got me thinking single phase. I suppose you can use 3 wire w/g SER for 3 phase service conductors but you better show me some engineering about what your anticipated L-N loads are going to be. If we are going to see any significant reactive loads on the neutral you are probably going to have to put in a larger <than phase> neutral.