ECN Electrical Forum - Discussion Forums for Electricians, Inspectors and Related Professionals
ECN Shout Chat
ShoutChat
Recent Posts
Using THWN on automotive circuits
by BigB - 03/23/23 11:19 AM
Continuous load
by HotLine1 - 03/08/23 02:11 PM
How's all our Non-US folks doing?
by dsk - 03/08/23 11:56 AM
Old Computers?
by Bill Addiss - 03/04/23 05:06 PM
New in the Gallery:
Burger King crown sillyness
Burger King crown sillyness
by wa2ise, December 11
240/208 to a house
240/208 to a house
by wa2ise, October 9
Who's Online Now
0 members (), 28 guests, and 17 robots.
Key: Admin, Global Mod, Mod
Previous Thread
Next Thread
Print Thread
Rate Thread
#90222 11/03/04 02:01 AM
Joined: Aug 2001
Posts: 545
A
aldav53 Offline OP
Member
Are plastic boxes ok to use in commercial buildings? Some do have a knockout for pipe or mc cable to run into.


The Golden Rule - "The man with the gold makes the rule"
Stay up to Code with the Latest NEC:


2020 NEC & Related Reference & Study Guides
2020 NEC & Related Reference & Study Guides
Pass Your Exam the FIRST TIME with these Exam Prep Combos:
 

>> Master Electrician Exam Prep     >> JourneyMan Electrician Exam Prep
 

Joined: Nov 2003
Posts: 269
E
Member
Non-metallic boxes cannot be used with metallic wiring methods unless meeting one of the two exceptions. 314.3.


John
Joined: Aug 2001
Posts: 545
A
aldav53 Offline OP
Member
Why then is there a 1/2" knockout? for PVC? What would be wrong with plastic boxes, there used in homes?


The Golden Rule - "The man with the gold makes the rule"
Joined: Apr 2002
Posts: 558
C
Member
The non-metalic boxes with standard K.O’s are for ENT (smurf tube) or can be used with RNMC. There is nothing wrong with non-metallic boxes when used with non-metallic wiring methods. You can’t use metal raceways or cable armors with non-metallic boxes since the raceway or armor would not be properly bonded.

Curt


Curt Swartz
Joined: Aug 2001
Posts: 545
A
aldav53 Offline OP
Member
caselec,
Yes true, unless you run metal cable from a bonded metel panel to the plastic box, then its bonded at one end.


The Golden Rule - "The man with the gold makes the rule"
Joined: Feb 2003
Posts: 198
Z
Member
electricman2 has the correct response.
I wonder if a twin M/C connector would satisfy the exception to 314.3?


Shoot first, apologize later.....maybe

Link Copied to Clipboard
Featured:

Tools for Electricians
Tools for Electricians
 

* * * * * * *
2023 National Electrical Code (NEC)
2023 NEC Now Available!
 
* * * * * * *

2020 Master Electrician Exam Preparation Combos
2020 NEC Electrician
Exam Prep Combos:
Master / Journeyman

 

Member Spotlight
mxslick
mxslick
Atomic City, ID USA
Posts: 806
Joined: October 2004
Top Posters(30 Days)
BigB 3
triple 2
Popular Topics(Views)
305,112 Are you busy
233,510 Re: Forum
218,193 Need opinion
Powered by UBB.threads™ PHP Forum Software 7.7.5