Using a sub feed lug #89971
10/26/04 09:48 AM
10/26/04 09:48 AM
N
Norstarr  Offline OP
Member
Joined: Sep 2004
Posts: 86
Wi
Have a 100 amp main breaker panel in a residence. Have to add a sub panel and plan to feed it with #4's and use a sub feed lug instead of a breaker. The sub panel is then protected by the 100 amp main breaker. Any code violation here?
Ron

2017 / 2014 NEC & Related Books and Study Guides
Re: Using a sub feed lug #89972
10/26/04 10:30 AM
10/26/04 10:30 AM
W
winnie  Offline
Member
Joined: Sep 2003
Posts: 649
boston, ma
I would double check the stab ratings on the main panel that is feeding the sub. Some panels limit the maximum current ratings of loads connected to a single bus stab.

Also the use of #4s falls right onto an ugly bit of NEC 310.15(B)(6). #4Cu is permitted to be protected with a 100A OCPD when it is used to supply the _main_ power feed of a single residence. #4Cu does not have sufficient ampacity to be protected at 100A _in general_, but for the specific load described in 310.15(B)(6) it is permitted to do so. This means that #4Cu is _not_ sufficient for the feed to a 100A subpanel.

But there is yet another exception, which is that the feed to any subpanel in a residence is not required to be larger than the main feed. So I think that using the #4Cu as you describe will be okay until such time as the main service is upgraded, at which point you will need to protect the subpanel at less than 100A.

-Jon


Featured:

2017 Master Electrician Exam Preparation Combos
2017 NEC Electrician
Exam Prep Combos:
Master / Journeyman

 

Member Spotlight
Niko
Niko
Campbell, CA
Posts: 356
Joined: August 2006
Show All Member Profiles 
Top Posters(30 Days)
Popular Topics(Views)
254,412 Are you busy
190,661 Re: Forum
180,384 Need opinion
Powered by UBB.threads™ PHP Forum Software 7.6.1
(Release build 20180101)
Page Time: 0.018s Queries: 14 (0.004s) Memory: 0.9428 MB (Peak: 1.0611 MB) Zlib enabled. Server Time: 2019-04-18 14:35:53 UTC