#89629 10/10/04 02:31 PM
Joined: Aug 2001
Posts: 599
N
Nick Offline OP
Member
Does anyone see an issue with running 480V 4000V Busduct under a raised floor? The floor does is conditioned and the busduct would be fully enclosed, just as if it were abouve the ceiling.
BTW: This access floor does not fall under article 645.

Horizontal Ad
#89630 10/12/04 12:47 AM
Joined: May 2003
Posts: 2,876
E
e57 Offline
Member
If the floor space is accessable for the lenght of the duct, I don't see why not, others may not agree.....


Mark Heller
"Well - I oughta....." -Jackie Gleason
#89631 10/12/04 07:02 AM
Joined: Mar 2002
Posts: 582
R
Ron Offline
Member
As long as the busway fits within the limitations of 300.22(C)(1), then it's fine.


Ron

Link Copied to Clipboard
Advertisement:-Right


Tools for Electricians
Tools for Electricians
 

Member Spotlight
The_Lightman
The_Lightman
Orlando, Fl, USA
Posts: 49
Joined: August 2001
Top Posters(30 Days)
Popular Topics(Views)
363,815 Are you busy
286,725 Re: Forum
265,159 Need opinion
New Page 2
Powered by UBB.threads™ PHP Forum Software 7.7.5