G
Member
I don't think you will have any problems operating the overcurrent device with the down sized ground. I would just pigtail the grounding wire and get on with my life. It is all you have. Like another poster said, if you really think you will be losing sleep over it, put them on a GFCI. That downsized ground will certainly be enough to trip a GFCI.


Greg Fretwell
Work Gear for Electricians and the Trades

Workgear for Electricians

#89625 10/12/04 07:07 PM
Joined: Jun 2004
Posts: 613
S
Member
Thanx for the replies...1st,I don't think the "grandfathered" rule would apply once I change the 2 prong style plugs to the currently used 3 prong style plugs since an upgrade is taking place with the installation of new grounded style recepticles.
But, I wasn't sure if the reduced size grounding wire in the old romex was acceptable for grounding when the code (250.122)specifies a #14 copper equipment ground to be used on 15 amp circuits.
Also at the main panel I'll have to unwrap the ground from under the metal romex clamp and connect it directly to the ground bar,as well as unwrapping the ground wire at each outlet box from under the box clamp and splicing them together and pigtail to the box and also to the device itself.Right?
Or can I just ground the device to the box and leave the grounds as they were originally installed in the 1960's?

#89626 10/12/04 08:43 PM
Joined: Apr 2004
Posts: 201
Member
Quote
Or can I just ground the device to the box and leave the grounds as they were originally installed in the 1960's?
You can but the Code did not permit the installation in that manner when it was installed (at least I don't think it did).
Quote
Also at the main panel I'll have to unwrap the ground from under the metal romex clamp and connect it directly to the ground bar, as well as unwrapping the ground wire at each outlet box from under the box clamp and splicing them together and pigtail to the box and also to the device itself. Right?
Again IMHO, you are correct. [Linked Image]

- - - - - - - - - - - - - - - - - - - - - - - - - - -
Charlie Eldridge, Indianapolis, Utility Power Guy


Charlie Eldridge, Indianapolis Utility Power Guy
#89627 10/12/04 09:02 PM
Joined: May 2003
Posts: 2,876
E
e57 Offline
Member
Sorry Charlie, I spaced your first post.


Mark Heller
"Well - I oughta....." -Jackie Gleason
#89628 10/12/04 10:44 PM
Joined: Apr 2004
Posts: 201
Member
No problem, I made a mistake just last year. [Linked Image]

- - - - - - - - - - - - - - - - - - - - - - - - - - -
Charlie Eldridge, Indianapolis, Utility Power Guy


Charlie Eldridge, Indianapolis Utility Power Guy