I am currently remodeling office space, I have an existing 8/3 AC cable that runs from a panel 125' to a kitchenette.

I plan to use this 8/3 AC as a multiwire branch circuit to feed a 120 volt 3000 watt water heater, the other side of this circuit will feed a 20 amp receptacle for a refrigerator.

This will mean I will have a single pole 35 and a single pole 20 feeding this multiwire branch circuit.

I see no problem with this, however my coworkers think I am nuts, and who would know that better then them. [Linked Image]

Am I missing something, is this a NEC violation?

Any responses are appreciated.

Thanks, Bob


Bob Badger
Construction & Maintenance Electrician
Massachusetts
Stay up to Code with the Latest NEC:


2020 NEC & Related Reference & Study Guides
2020 NEC & Related Reference & Study Guides
Pass Your Exam the FIRST TIME with these Exam Prep Combos:
 

>> Master Electrician Exam Prep     >> JourneyMan Electrician Exam Prep
 

Joined: Jan 2004
Posts: 1,507
G
Member
Bob I think you comply with 210.4(C) and I assume that the common conductor of the circuit is insulated and that there is also an equipment grounding conductor. Where do I put the green sticker?


George Little
Joined: Nov 2003
Posts: 269
E
Member
Go for it. Nothing says that the OCPD's have to be equal. [Linked Image]


John
Joined: Sep 2003
Posts: 650
W
Member
I know that this is picking nits, but if you use a #8 Cu for a 20A circuit, wouldn't you also be required to use #8 for the EGC? *grin* Of course, given your normal work situation, I'm guessing that this circuit is in pipe.

-Jon

Joined: Jan 2003
Posts: 4,391
I
iwire Offline OP
Moderator
George, yes I have a white insulated grounded conductor. [Linked Image]

electricman2 That is my thinking too. [Linked Image]

Jon, I do not think you are nit picking, you are right on the money IMO.

If this was 8/3 MC cable the EGC would be 10 AWG which as you point out would be to small for the 20 amp circuit per 250.122(B)

This happens to be 8/3 AC cable, type AC cable does not have a copper EGC at all, it utilizes the armor as the EGC. [Linked Image]

Thanks for the replies

Bob


Bob Badger
Construction & Maintenance Electrician
Massachusetts

Link Copied to Clipboard
Featured:

Tools for Electricians
Tools for Electricians
 

* * * * * * *
2023 National Electrical Code (NEC)
2023 NEC Now Available!
 
* * * * * * *

2020 Master Electrician Exam Preparation Combos
2020 NEC Electrician
Exam Prep Combos:
Master / Journeyman

 

Member Spotlight
Niko
Niko
Campbell, CA
Posts: 356
Joined: August 2006
Top Posters(30 Days)
triple 2
Popular Topics(Views)
303,310 Are you busy
232,264 Re: Forum
217,021 Need opinion
Powered by UBB.threads™ PHP Forum Software 7.7.5