ECN Electrical Forum - Discussion Forums for Electricians, Inspectors and Related Professionals
ECN Shout Chat
ShoutChat
Recent Posts
Broken Outlet & Dangling Light
by LoneWolf - 06/14/21 08:21 PM
How's all our Non-US folks doing?
by C-H - 06/14/21 05:42 PM
Where is Everyone?
by Bill Addiss - 06/14/21 12:37 PM
Conduit over Vinyl Siding
by Bill Addiss - 06/14/21 12:35 PM
Switched Receptacles -Top or Bottom?
by Bill Addiss - 06/14/21 12:25 PM
New in the Gallery:
2020 - 2021 Winter Project
2020 - 2021 Winter Project
by Bill Addiss, April 29
Garden 2021
Garden 2021
by Bill Addiss, April 26
Who's Online Now
0 members (), 44 guests, and 19 robots.
Key: Admin, Global Mod, Mod
Previous Thread
Next Thread
Print Thread
Rate Thread
Joined: May 2004
Posts: 3
M
Junior Member
I'm getting differing opinions on the interpretation of Note 2 to Table 450.3(B). I have a 150 kVA, 480-208Y/120 V indoor dry-type transformer feeding three main breaker panelboards. The question comes from the phrase in Note 2 "shall not exceed the allowed value of a single overcurrent device". Is that value for multiple overcurrent devices (a) strictly a maximum of 125% of transformer rated current, or (b) permitted to be as high as "the next higher standard rating" of Note 1 of Table 450.3(B). If "value" means (a), the sum of the three main breakers is limited to 520 A, but if "value" means (b), I can go to 600 A.

2017 / 2014 NEC & Related Books and Study Guides
Joined: Nov 2000
Posts: 2,148
R
Member
Mike,
The value is per note 1, in my opinion. This permits the rounding up to a total of 600 amps for the three overcurrent protective devices. Don't forget that the conductors between the transformer and the panles must be protected per 240.21(C).
Don


Don(resqcapt19)
Joined: Aug 2003
Posts: 1,374
R
Moderator
There is an interesting change to this in the 2005.


Ryan Jackson,
Salt Lake City
Joined: Jan 2003
Posts: 4,391
I
Moderator
Quote
There is an interesting change to this in the 2005.

Ryan is such a code teaser. [Linked Image]

Come on and give it up. [Linked Image]


Bob Badger
Construction & Maintenance Electrician
Massachusetts
Joined: Aug 2003
Posts: 1,374
R
Moderator
240.21(C) in the 2005 now says that you cannot use 240.4(B) on the secondary side.


Ryan Jackson,
Salt Lake City
Joined: May 2004
Posts: 162
C
Member
If I'm reading note two correctly it appears to only apply if the primary overcurrent protection is sized larger than 125% of the pri FLA?? In that are compelled to additionally protect the secondary winding.

If the pri OCPD is sized to protect the transformers pri. per 450.3 (B) [pri protection only} , then OCP for the secondary winding is not required.

You may have multiple taps from the secondary of the transformer (as mentioned 240.21 (C) ) to several loads the secondary conductors must be protected per that section and article 240.
If your pri overcurrent protection exceeds 225 A (480/.83)I think Note two is applicable.??


RYAN could you indicate the paragraph in the 05 that references 240.4 I'm looking at the pre-print and appear to be missing it!!

charlie

[This message has been edited by cpal (edited 09-17-2004).]

Joined: May 2004
Posts: 3
M
Junior Member
Thanks for all of the feedback. In the end, the local AHJ said we had to stick strictly with 125%; next larger size denied. Sounds like the 2005 NEC will make all of the discussion go away.

Joined: Aug 2003
Posts: 1,374
R
Moderator
From the 2005:

240.21(C) Transfomrer secondary conductors. Each set of conductors feeding seperate loads shall be permitted to be connected to a transformer secondary, without overcurrent protection at the secondary, as specified in 240.21(C)(1) through (C)(6). The provisions of 240.4(B) shall not be permitted for transformer secondary conductors.


*(C)(1)through(C)(6) are the 10', 25', etc., rules, similiar to the 2002.


Ryan Jackson,
Salt Lake City
Joined: May 2004
Posts: 162
C
Member
Thanks Ryan

The reference to 240.4 (B) was accepted in Comment stage and not in the pre-print.

charlie


Link Copied to Clipboard
Featured:

Tools for Electricians
Tools for Electricians
 

* * * * * * *

2020 Master Electrician Exam Preparation Combos
2020 NEC Electrician
Exam Prep Combos:
Master / Journeyman

 

Member Spotlight
The_Lightman
The_Lightman
Orlando, Fl, USA
Posts: 49
Joined: August 2001
Top Posters(30 Days)
Admin 13
Trumpy 10
Popular Topics(Views)
280,356 Are you busy
213,431 Re: Forum
200,352 Need opinion
Powered by UBB.threads™ PHP Forum Software 7.7.5