Kitchen Receptacles #89276 09/08/04 02:47 PM
Joined: Jan 2004
Posts: 1,507
G
George Little Offline OP
Member
I am inspecting a commercial "Kitchen". The plans call it a "Warming Kitchen" There is no cooking performed in this room. Food is cooked off site and brought to this "Warming Kitchen" and stored in stainless steel cabinets that are the size of refrigerators. These cabinets (about 15 of them) are on wheels and have cords that plug in for warming or cooling. The room is about 50 feet square or for you metric guys 15m square. The question of the day is- Do I need to ask the contractor to comply with 210.8(B)?


George Little
2017 / 2014 NEC & Related Books and Study Guides
Re: Kitchen Receptacles #89277 09/08/04 03:56 PM
Joined: Jun 2003
Posts: 1,143
D
DougW Offline
Member
Any dishwashers / scrub sinks?

Re: Kitchen Receptacles #89278 09/08/04 04:37 PM
Joined: Feb 2002
Posts: 375
G
George Offline
Member
(5.5 sq meters)

Re: Kitchen Receptacles #89279 09/08/04 05:01 PM
Joined: Jun 2004
Posts: 220
T
trekkie76 Offline
Member
I don't see a definition for a kitchen, but if your calling it a kitchen, I would say yes to 210-8(b).

Re: Kitchen Receptacles #89280 09/08/04 05:35 PM
Joined: Aug 2003
Posts: 1,374
R
Ryan_J Offline
Moderator
From what I have read, the 2005 will define kitchen as "an area with a sink and permanant provisions for cooking".

I would base my decision off af that.


Ryan Jackson,
Salt Lake City
Re: Kitchen Receptacles #89281 09/08/04 05:46 PM
Joined: Jun 2004
Posts: 220
T
trekkie76 Offline
Member
how can you base an inspection on a definition that hasen't been published yet? The inspection has to be based on the code being enforced at the time of inspection. Unless the EC wants to wait until 2005.

Re: Kitchen Receptacles #89282 09/08/04 06:04 PM
A
Anonymous
Unregistered
IMHO....
It seems to me that any place the code requires GFCI protection is a place where there is a likely opportunity that there is a chance to come in contact with only the hot conductor and another grounded surface as in metal water pipe, damp earth, concrete etc. If the likelyhood is not there I do not see a reason for the GFCI protection. So if this room has water proofed walls and wall covering with water proof floors and a floor drain and they intend to clean it with a hose..... Well, your the inspector! Please post back on your decision.

Re: Kitchen Receptacles #89283 09/08/04 06:43 PM
Joined: Jan 2004
Posts: 1,507
G
George Little Offline OP
Member
Okay, I've heard from the masses and I have decided that based on the definition of a kitchen as found in Websters "n : a room equipped for preparing meals" That this is not a kitchen. So based on the '02 Code, they don't need GFCI protection on the receptacles. This area as I discribed in my orginal post is only used to store food and maintain temperature of food either hot or cold.


George Little
Re: Kitchen Receptacles #89284 09/08/04 06:46 PM
Joined: Jul 2004
Posts: 625
S
SolarPowered Offline
Member
Quote
There is no cooking performed in this room.

Yeah. Right. When pigs fly.

Sounds to me like it's a kitchen.

Re: Kitchen Receptacles #89285 09/08/04 07:44 PM
Joined: Jan 2004
Posts: 1,507
G
George Little Offline OP
Member
The expression is "When donkeys fly"


George Little
Page 1 of 2 1 2

Featured:

2020 National Electrical Code
2020 National Electrical
Code (NEC)

* * * * * * *

2020 Master Electrician Exam Preparation Combos
2020 NEC Electrician
Exam Prep Combos:
Master / Journeyman

 

Member Spotlight
Joe Tedesco
Joe Tedesco
Boston, Massachusetts USA
Posts: 2,749
Joined: October 2000
Show All Member Profiles 
Top Posters(30 Days)
Trumpy 20
Popular Topics(Views)
272,213 Are you busy
206,102 Re: Forum
194,100 Need opinion
Powered by UBB.threads™ PHP Forum Software 7.7.3