BX in a MEDICAL Facility #89038 08/26/04 02:02 PM
Joined: Feb 2004
Posts: 494
M
mustangelectric Offline OP
Member
Is BX or MC cable allowed in a rural medical clinic with patient exam rooms and xray? wood structure single story

If I remeber correctly it is NOT.

thanks for any reply

2017 / 2014 NEC & Related Books and Study Guides
Re: BX in a MEDICAL Facility #89039 08/26/04 04:52 PM
Joined: Jun 2004
Posts: 220
T
trekkie76 Offline
Member
517-2 def. of a health care facilities.it includes a clinic. 517-13(a) lists MC as an acceptable wiring method, as long as it's outer metal sheath is identified as a grounding path. the MC cable has to have an insulated ground in it. It is usually called Hospital grade, and has a green paint on it.

[This message has been edited by trekkie76 (edited 08-26-2004).]

Re: BX in a MEDICAL Facility #89040 08/26/04 06:05 PM
Joined: Jan 2003
Posts: 4,391
I
iwire Offline
Moderator
Very unlikely you will get MC with a sheath that is an acceptable grounding conductor, I use MC all the time and have never seen the type of MC that has the right kind of armor for grounding.

What you need is hospital grade AC cable.

The outer armor is a listed grounding conductor along with the added green grounding conductor.


Bob Badger
Construction & Maintenance Electrician
Massachusetts
Re: BX in a MEDICAL Facility #89041 08/27/04 06:23 AM
Joined: Sep 2003
Posts: 650
W
winnie Offline
Member
Would there be any difference between hospital grade AC and hospital grade MC...other than the 'red hat' requirement [Linked Image]

-Jon

Re: BX in a MEDICAL Facility #89042 08/27/04 08:05 AM
Joined: May 2002
Posts: 1,716
R
Roger Offline
Member
Jon, there is no such thing as HG MC.

Also remember that HCFC can not be used for Emergency Branch wiring.

Roger

Re: BX in a MEDICAL Facility #89043 08/27/04 09:47 AM
Joined: Jun 2004
Posts: 206
C
capt al Offline
Member
Jon look at 250.118 (9) and 250.118 (11). That will explain the difference between AC & MC. Hospital grade Mc I'm told is custom order. Probably explains why I and iwire have not seen it.

Re: BX in a MEDICAL Facility #89044 08/27/04 11:26 AM
Joined: May 2002
Posts: 1,716
R
Roger Offline
Member
Capt al, once again there is no such thing as hospital grade MC. There is MC with a sheath that is recognized as a ground per 250.118, and it is allowed for redundant grounding per 517.13, but that is not a Health Care Facility Cable.

Type HCFC is a true Armored Cable.

Go here for more info

Roger



[This message has been edited by Roger (edited 08-27-2004).]

Re: BX in a MEDICAL Facility #89045 08/27/04 03:39 PM
Joined: Jun 2004
Posts: 220
T
trekkie76 Offline
Member
well then, someone should start making Hospital grade MC becuase it is listed as a wiring method in 517-13a. Just because you have never seen it doesn't mean it can't be used or doesn't exist.

Re: BX in a MEDICAL Facility #89046 08/27/04 05:33 PM
Joined: May 2002
Posts: 1,716
R
Roger Offline
Member
Trekkie, did you check the link I posted?

As far as MC meeting the requirements of 517-13 (99 NEC reference) some types can meet this requirement and the smooth type is one of these, but this still is not a "Hospital Grade" cable.

Yes, I have seen the smooth type MC, and you have too most likely. Some appliances have it installed from the factory, but as Iwire says it is not common in our field.

And I will say again, Hospital Grade MC does not exist, HCFC is an AC hybrid. [Linked Image]

Roger

Re: BX in a MEDICAL Facility #89047 08/27/04 06:45 PM
Joined: Jun 2004
Posts: 220
T
trekkie76 Offline
Member
the original post asked if mc was acceptable as a wiring method in a hospital. it is

Page 1 of 2 1 2

Featured:

2020 National Electrical Code
2020 National Electrical
Code (NEC)

* * * * * * *

2020 Master Electrician Exam Preparation Combos
2020 NEC Electrician
Exam Prep Combos:
Master / Journeyman

 

Member Spotlight
sparky66wv
sparky66wv
West Virginia
Posts: 2,236
Joined: November 2000
Show All Member Profiles 
Top Posters(30 Days)
Trumpy 20
Popular Topics(Views)
272,256 Are you busy
206,143 Re: Forum
194,135 Need opinion
Powered by UBB.threads™ PHP Forum Software 7.7.3