Joined: Oct 2000
Posts: 2,749
Member
Rule always said: "358.12 Uses Not Permitted.
EMT shall not be used under the following conditions:
(1) Where, during installation or afterward, it will be subject to severe physical damage."


Joe Tedesco, NEC Consultant
Stay up to Code with the Latest NEC:


2020 NEC & Related Reference & Study Guides
2020 NEC & Related Reference & Study Guides
Pass Your Exam the FIRST TIME with these Exam Prep Combos:
 

>> Master Electrician Exam Prep     >> JourneyMan Electrician Exam Prep
 

Joined: Nov 2000
Posts: 2,148
R
Member
Only the AHJ knows!


Don(resqcapt19)
Joined: May 2004
Posts: 697
D
Member
I think where it might get hit with a snowplow would qualify.

Dave

Joined: Feb 2004
Posts: 1,438
Member
Is corrosion considered "physical damage"?

-Randy

Joined: Apr 2002
Posts: 2,527
B
Moderator
Snowplows and forklifts.

Isn't the time aspect, "...during installation or afterward..." a more recent addition to the rule? Before—always was just implied, I suppose.




[This message has been edited by Bjarney (edited 07-13-2004).]

Joined: May 2002
Posts: 1,716
R
Member
Well here is an example I think is understandable (atleast as much as we have per the NEC)

[Linked Image from click-smilies.de]

On the left I think we have "physical damage"
On the right we are probably looking at closer to "severe physical damage"

[Linked Image]

Roger

Joined: Jun 2003
Posts: 681
P
Member
Joe
We have been mulling that over here for a while, and come up with the AHJ decision as well - but that doesn't bode well for some guys who have to deal with the ' ' inspector type.

Very good Roger [Linked Image]

Pierre


Pierre Belarge
Joined: May 2002
Posts: 1,716
R
Member
Thanks Pierre. [Linked Image] I hope you and the new company are doing well.

How is your better half doing?

Roger

Joined: Nov 2002
Posts: 558
G
Member
My guess is,it'd be a common-sense type of thing. If it's in an area with vehicle traffic,EMT's probably a bad idea.

Russell

Joined: Apr 2002
Posts: 7,333
Likes: 7
Member
AS an inspector....I honestly could not differentiate "severe" and "regular" physical damage.

Is 'severe' damage the EMT being flattened to 1/8" thickness? Damage is damage I would have to say. Determining future possibilities for damage has to be a basic common sense move on the EC's part.

Joe; you picked a real good point!!

John


John
Page 1 of 2 1 2

Link Copied to Clipboard
Featured:

Tools for Electricians
Tools for Electricians
 

* * * * * * *
2023 National Electrical Code (NEC)
2023 NEC Now Available!
 
* * * * * * *

2020 Master Electrician Exam Preparation Combos
2020 NEC Electrician
Exam Prep Combos:
Master / Journeyman

 

Member Spotlight
noderaser
noderaser
Portland, Oregon, United States
Posts: 404
Joined: March 2007
Top Posters(30 Days)
triple 3
Popular Topics(Views)
303,230 Are you busy
232,223 Re: Forum
216,961 Need opinion
Powered by UBB.threads™ PHP Forum Software 7.7.5